    On a side note alot of those ductless splits are variblespeed compressors and fans so checking subcooling and superheat are out of the question based on the varible speed part of it. weighing the charge is the best method...... On those type of systems that is.

  2. #41
    Join Date
    Feb 2009
    Location
    Auglaize County, Ohio
    Posts
    56
    Post Likes
    Quote Originally Posted by john_ertw View Post
    I was home during the install. I was there at the start to ensure they got off to a good start with locating all the equipment and everything looked good. I did occasional checks throughout the day to ensure everything was proceeding and nothing looked out of wack. During the setup of equipment I ended up sticking around the whole time. I helped the tech figure out how to wire the VisionPro IAQ thermostat (he asked me to) since he only installed one or two before (I actually corrected some of the wiring he did, i.e. the humidifier was wired wrong and did not work until I told him how to wire it). As I was there I'm sure all of the items I listed weren't done.

    I asked questions about certain items and one of them had to do with pulling a vacuum. The tech showed me the gauge and explained how he pulled a vacuum to -30 psi (the lowest reading on the gauge). He kept the pump on for a while after reaching -30 psi. He then closed off the system, turned off the pump and released the refrigerant. He didn't keep the vacuum without the pump, so there is no way to know if there was a leak since the pump would keep pulling air out.



    Luckily Goodman installs a filter drier at the factory. Hopefully it is enough! What problems can moisture in the system cause?
    OK, first after all fitting were brazed shut. The tech should of put nitrogen in and took the pressure up to about 150 psi and wait about 30 min. If the gauge doesnt move then realease the nitrogen and pull the system in to a vacuum of at least 500 microns. Once reached let it set and watch the micron gage and see if it goes up. If it doesnt with it being a new install it shouldnt. Release the refrigerant and you are set to go.
    Last edited by kajer; 06-21-2009 at 10:38 PM. Reason: miss spell
    Semper Fi

  3. #42
    Join Date
    Jan 2009
    Location
    Ypsi. Mi.
    Posts
    198
    Post Likes
    You still need to check superheat or subcooling.If you have a long line set you will need to add some freon.The factory may have shorted the system it never hurt`s to check the charge on a unit.

  4. #43
    Join Date
    Jun 2009
    Location
    Somewhere in the airconditioned world!
    Posts
    20
    Post Likes
    Is this really a new install? Tape on the TXV? Ahh... Anyways, definitely check superheat to make sure the TXV is working properly. Might want to give that company back a call.

  5. #44
    Join Date
    Aug 2008
    Location
    Toronto, Ontario, Canada
    Posts
    147
    Post Likes
    I finally got around to calling the owner. The a/c has been performing well, but who knows if it is performing optimally.

    I explained that I had concerns that the tech did not check a/c subcooling, used tape for the TXV bulb, and did not check the furnace's temperature rise or clock the BTU/hour usage.

    I did not bother mentioning anything about a deep vacuum not being taken because I figured they can't do that if they don't have the proper equipment. I am kind of hoping that there was no moisture in the new lineset or other parts and that the filter-dryer does its job. Any disagreement here? What would you do?

    He said he will send a different tech to do the checks. He thanked me for bringing it to his attention and said the tech that did the install is an excellent tech. He told me that he has seen the tech do all of these check several times in the past and was a little surprised.

    I was expecting a bit of a fight, but he was quick to say he will send someone to do all the checks. Hopefully everything works out.

    Anything to look out for when the new tech comes by? I want to let him do his job, but I don't want to obtain a new set of problems.

  6. #45
    Join Date
    Aug 2008
    Location
    Toronto, Ontario, Canada
    Posts
    147
    Post Likes
    Does the CFM the blower is pushing make a difference in the subcooling value read? For example will my system have the same subcooling value if it is read when the blower is pushing 350 CFM and when the blower is pushing 450 CFM if all other variables are kept constant?

    The reason I ask is that my system is currently set to push 1100 CFM for a 2.5 ton (440 CFM/ ton instead of the standard 400 CFM/ton). This is in to allow it to push some air to the 2nd floor of my house (2800 sq ft not including the basement). It seems that if my house was in the southern states I would have a much larger a/c requiring more air flow which will allow more of it to reach the 2nd floor.

  7. #46
    Join Date
    Jun 2009
    Location
    London Ontario
    Posts
    116
    Post Likes

    Words to live by

    Quote Originally Posted by mb20fan View Post
    You still need to check superheat or subcooling.If you have a long line set you will need to add some freon.The factory may have shorted the system it never hurt`s to check the charge on a unit.
    Factories do undercharge some units, and overcharge others, it,s not really a big deal for the installer, but refer to the quote above.