    any heard of installing a 2.5 ton compressor with a 3 ton air handler? why would someone do that instead of matching the 2.5 ton compresor with a 2.5 air handler. won't the cfm's be to high with the 3 ton handler, 1200 instead of 1000.
    Nov 2008
    Chapel Hill, NC
    The CFM is usually adjustable (from ~600 to ~1200 in a 3 ton AH). The coil should be matched, though.
    Quote Originally Posted by fishin View Post
    I've seen it done both ways. And both ways work. If you know what the end results you want are
    Jun 2006
    Omaha, Nebraska
    Fellow techs have said they will sometimes use a larger evap coil because it gives more surface area for condensation. I have never decided to try it. If there were an issue then I'd be SOL with the warranty.
    May 2009
    So Cal
    You will also see this in some of the AHRI numbers to increase the efficiencies to meet the Tax Credit standards.
    Its how some manufacturers get their SEER rating.
    Common practice. Nothing wrong with it.
    DC Metro Area (MD)
    Quote Originally Posted by man from trane View Post
    Not if it's an acceptable match, as it often is. For example Carrier's 25HCB336A003 is an approved match with the FX4CNF036000 and FX4CNF042000.
    Jun 2006
    Omaha, Nebraska
    That's good to know. Thanks!
    With all the hacks where I live, I usually see the opposite- 5 Ton condensing unit on a 4 Ton evap. Not efficient, but it works.