    NO place for HVAC in Green home

    We are Owner/Builders.

    We designed our new 2 story home to allow for duct work inside 14" and 18" floor truss systems. The unit would sit inside our single story kitchen attic and connect through a single wardrobe (We used wardrobes instead of closets) in our master bedroom and then fit perfectly inside our truss systems for delivery to the rest of the house. The master bedroom is on the second floor.

    Unfortunately, due to a series of early setbacks in other areas, no one thought to make sure that the truss designer, even though he was aware of our HVAC intentions, left a clear path in his trusses for the duct work - BIG LESSON LEARNED. Every path seems to be completely blocked or too small to handle the standard ducts needed.

    Our HVAC contractor has come up with only one way to put in the standard ductwork. He wants to hide the duct work in at least THREE large spots inside our master wardrobes AND he has to add a 3 foot chase to an adjoining room. We are deeply concerned, not to mention disappointed that this will kill our closet space and appraisal value.

    Our home uses passive solar design and we've selected an 18 SEER amana with a lifetime warranty. We selected this unit after determining several months ago that a Daikin was out of our price range. Now we've signed a contract with an HVAC contractor who doesn't handle Daikin and so I'm not sure that's an option any more. We've been looking into the spacepak products, but along with some noise issues, our contractor is saying the ducting and handlers are 40% more expensive and that our 18 seer would be reduced to a 13.

    Our new home is 2500 square feet plus another 1000 in the attic which we plan to cool separately. We will have an insulated envelope that includes attics and a sealed crawlspace that vents into the house and mixes with the indoor air (a vapor barrier will be installed down there). Insulation is 6" of spray in foam, rigid foam, osb and siding on the walls. The roof is spray foam, attic wrap, osb/radiant barrier decking and regular shingles. We are located in north central Texas in a mixed humid climate.

    Here's what we contracted the HVAC guy to install before we realized we had a space issue.
    Amana - ASZ18036 heat pump 3 ton 18 SEER
    Amana – AEPF3036 Variable speed fan coil unit with 10kw Aux heat and TXV
    Honeywell – HK322 Zone control panel
    Honeywell - Zone dampers
    Honeywell programmable thermostats
    Filter system with UV
    ERV system
    R-8 duct
    Copper line sets

    We've worked for three years on this project and the web trusses were always our plan for duct work, electrical, plumbing etc. We experienced a series of early setbacks during construction and checking for a path just got overlooked. The HVAC setup is intergral to our whole house design, both in function and placement.

    Help.
    Thanks!!!

  2. #2
    Join Date
    Jun 2004
    Location
    Howell, Michigan
    Posts
    16,396
    Post Likes
    I have never seen a good duct system that was installed up into a truss system because of space concerns. Each and every one was a compromise with poor results.

  3. #3
    Join Date
    Apr 2008
    Location
    TEXAS
    Posts
    1,706
    Post Likes
    ditto
    "When the people find they can vote themselves money,that will herald the end of the republic" - Benjamin Franklin

    "Government is not reason, it is not eloquence, it is force;like fire, a troublesome servant and a fearful master. Never for a moment should it be left to irresponsible action"- George Washington

  4. #4
    Join Date
    May 2006
    Location
    Raleigh,NC.
    Posts
    573
    Post Likes

    compromise is right

    10' flexible is the largest you can hope for and each (zone) and those supplies had better be sized and installed correctly because there's no going back to repair or damper adjustment. we have done quite a few with first floor and finished basement using two systems. you need a lot of mechanical room to get that maze run correctly. labor, labor and more labor. takes hours just to lay it out and draw it up and still there is a certain amount of boxing in to be done. your not going to like it but, if your contractor asks for some part of a room for ducting it's because he is trying to deliver the proper air flow. without that ,high seer just became lower. my favorite smart-a$$ saying is just draw some arrows on the wall a maybe the air will follow.i'm sorry, sounds like your'e trying to build the right way though. i wish you good luck without too much compromise.
    remember, with electronics; when its brown,its cooking and when its black, its done!!!

  5. #5
    Join Date
    Jul 2008
    Location
    Prairie du Sac, WI
    Posts
    22
    Post Likes

    No place for HVAC in Green home

    Look into a ductless heat pump/A/C system like Mitsubishi. No ductwork required, just two fluid lines. Could install 3-4 units per condensor I believe. Total cost may be more efficient than trying to get ductwork installed.

  6. #6
    Join Date
    May 2009
    Posts
    2
    Post Likes
    Thread Starter

    Thank You!

    Thank you to everyone. It looks as though we have finally found a good path for all the standard ductwork!!!

    I guess if you stare at web truss ceilings long enough, you eventually find a wy through - course we also moved the location of our unit and lost some bonus room square footage, but way better than cutting into wardrobe and primary rooms.

    Thanks again!

  7. #7
    Join Date
    Oct 2003
    Location
    las vegas
    Posts
    1,505
    Post Likes
    i have never worked on one or installed one but this maybe a candidate for a high velocity system. smaller ducts may be the answer.

  8. #8
    Join Date
    May 2009
    Location
    South of Heaven
    Posts
    1,407
    Post Likes
    I say go ..." exposed " ....radical twisted transitions , rectangular to round y branches , spiral round pipe...hey it was an idea not mentioned. And look at the drywall trees youd be saving ( lol ? ).

  9. #9
    Join Date
    May 2009
    Location
    Indiana
    Posts
    77
    Post Likes
    Consider a high velocity heating and cooling system using small diameter ducts that can be more easily threaded through floor, ceiling, and wall cavities. High velocity systems operate quietly and improve dehumidification, room air mixing, and energy efficiency over standard air-delivery duct systems.

    High velocity heating and cooling systems use a special fan coil and air handling unit that generates high pressure air forced through small diameter ducts. The main supply trunk is either a rectangular or round duct that supplies air to flexible, insulated, 2" diameter plastic feeder ducts. Air passes through sound-suppressing tubing at the end of a duct run before entering the room through a plastic collar fitting. Air is supplied at 440 to 1200 cubic feet per minute (CFM).

    High velocity systems use standard outdoor condensing units for air conditioning and heat pump systems. Adding a bank of electric heating elements to the air handler can provide heating capability to a high velocity air-conditioning system. High velocity system air handlers can satisfy cooling capacities between 18,000 and 60,000 BTUH and heating capacities between 24,000 and 143,000 BTUH.

    SpacePac and Unico are tow manufactures of high velocity systems.

  10. #10
    Join Date
    Aug 2007
    Location
    Eastern PA
    Posts
    21
    Post Likes
    How effective is the passive solar? Is the heat pump mainly there for cooling and supplement to the solar? You might want to consider a multizone ductless system.

  11. #11
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is online now Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,831
    Post Likes

    Mark? What's the SEER ratings for the hi velocity systems?

    He said he wants to get 18 SEER.

    PHM
    -------



    Quote Originally Posted by Mark T View Post
    Consider a high velocity heating and cooling system using small diameter ducts that can be more easily threaded through floor, ceiling, and wall cavities. High velocity systems operate quietly and improve dehumidification, room air mixing, and energy efficiency over standard air-delivery duct systems.

    High velocity heating and cooling systems use a special fan coil and air handling unit that generates high pressure air forced through small diameter ducts. The main supply trunk is either a rectangular or round duct that supplies air to flexible, insulated, 2" diameter plastic feeder ducts. Air passes through sound-suppressing tubing at the end of a duct run before entering the room through a plastic collar fitting. Air is supplied at 440 to 1200 cubic feet per minute (CFM).

    High velocity systems use standard outdoor condensing units for air conditioning and heat pump systems. Adding a bank of electric heating elements to the air handler can provide heating capability to a high velocity air-conditioning system. High velocity system air handlers can satisfy cooling capacities between 18,000 and 60,000 BTUH and heating capacities between 24,000 and 143,000 BTUH.

    SpacePac and Unico are tow manufactures of high velocity systems.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

  12. #12
    Join Date
    Dec 2005
    Location
    Indiana
    Posts
    309
    Post Likes
    Quote Originally Posted by Drippy View Post
    Look into a ductless heat pump/A/C system like Mitsubishi.
    Mitsubishi = Garbage. They have no tech support for when things go wrong. I talked to the "tech support" and they told me they were just some installers that awnser the phone. they ship the wrong parts, guess at trouble shooting....on and on... they are nice when they are running though

    I would look into Fujitsu minisplit. Not sure what you mean by a "green" home. That bandwagon has split off into many paths. if you are going green then just buy a solar powered fan and open the window (i saw these people on Dirty Jobs with Mike Rowe make a green home and they used cow poop insted of wood)

    If you're looking into low energy home, take a look at Fujitsu. 18 seer wall units. Also with a ductless system you get no static pressure noise, and zoning. only running the unit in the room your in is saving even more energy.

    http://www.fujitsugeneral.com/end_user_home.htm


    .
    Work sucks, lets go skydive

  13. #13
    Join Date
    Feb 2004
    Location
    SW Florida
    Posts
    1,271
    Post Likes
    HVAC as an afterthought? Good luck

  14. #14
    Join Date
    Jul 2008
    Location
    nw ohio
    Posts
    67
    Post Likes
    The company I work for has had great success with the Mitsubishi system including tech support out of Atlanta. We have had there tech support people just show up at our office wanting to spend a day looking at out jobs. The over the phone tech support is fast usually within a half hour or less.
    If you decide to go with Mitsubishi go with a Diamond dealer and designer it will give you a additional 5 year warranty.
    We have bid a job to replace a Diakin that has only been in 4 years at a college due to control issues and difficulty getting parts in our area.

  15. #15
    Join Date
    Jul 2008
    Location
    Rochester NY
    Posts
    5,298
    Post Likes
    Love my high velocity system. No stratification.

  16. #16
    Join Date
    Sep 2009
    Posts
    17
    Post Likes
    Quote Originally Posted by zzonko View Post
    HVAC as an afterthought? Good luck
    Exactly! Comfort comes first for creatures of habit like Humans!

  17. #17
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    We work with a builder who likes to use the Truss type joist, however he makes sure the duct space is lined up (when the joists are set) and we are there to slide the ductwork through the space BEFORE the other mechanical folks start. Otherwise it'll be a real crap shoot, and I really wish you luck with it! And I don't envy your HVAC contractor at this stage of the project. I wish you the best of luck!!

  18. #18
    Join Date
    Apr 2007
    Location
    NC
    Posts
    8
    Post Likes
    on the hi velocity systems, unico has an air handler with an advanced blower module, not variable speed but steps up. can be used with two stage.

  19. #19
    Join Date
    Apr 2007
    Location
    NC
    Posts
    8
    Post Likes
    utilizes a 9 inch supply trunk on 3 and half ton and down. 4 ton like to see 10 inch for at least 30 percent of main trunk. round duct.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •