Gas Equipment venting to an exterior metal chimney
I am looking for advice for venting a boiler and wh into an outside chimney 40 Ft high
the boiler is fan assisted 233 MBh and wh is Nat draft 75.1 MBH , total gas load 308 MBH
the outside design temp is 12 deg f
the chimney is not specified yet . a 7" interrnal type B vents works inside, but owner doesn't want to lose space.
i was going to spec a stainless steel chimney for outside
the only tables i can find in NFPA 54 are for exterior masonry chimneys and the and i cannot satisfy the minimum gas input in table for a 40 ft high chimney
-
09-22-2012, 03:47 PM #2
You need some kind of liner or you will condense the gases from both units. B vent down the chimney will be great.