    Another return question

    In the thread, Carrier vs. Am. Std., Robotec said:

    "If your supply registers are on the floor or low on the wall, then a ceiling return would be best."

    I also have a lack of return upstairs, especially with doors closed. In two bedrooms, I have a wall which is shared with the stairswell. Has it ever been done where a return grill would be cut in on the wall at the ceiling in the bedroom, then a similar grill placed at a lower level on the stairwell side? These would be located between studs.

    The location of the grills in the stairwell would favor the downstairs return grills, where there are 4, vs. 1 upstairs.

    Amp

  2. #2
    Join Date
    Dec 2003
    Posts
    709
    Do you mean just like a transfer grille where you put grille on either side of the wall to let the air into the hallway?

    You can do this, it is best to cut the one in the bedroom high and the on in the hall low to for privacy, but the wall stud cavity has to be open of course in between.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    68,058
    Probably do more harm then good.

    When the A/C shut off. It would have a chimney effect. And let the first floor heat rise into those rooms. making them worst then before.

    May also violate code.

    Since in a fire. The fire would be able to travel though that wall chase from the first floor to those second floor rooms even with the doors closed.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Feb 2007
    Posts
    999
    Quote Originally Posted by hivacer View Post
    Do you mean just like a transfer grille where you put grille on either side of the wall to let the air into the hallway?

    You can do this, it is best to cut the one in the bedroom high and the on in the hall low to for privacy, but the wall stud cavity has to be open of course in between.
    Yes, that is exactly what I mean.

    I'm looking at 'creative' ways to handle the other two bedrooms, other than over the doors.

    Amp

  5. #5
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Manual D says ,return location high or low has little effect on comfort,believe it or not.

  6. #6
    Join Date
    Mar 2008
    Location
    Long Beach, CA
    Posts
    3,384
    Quote Originally Posted by dash View Post
    ....believe it or not.
    NOT !!!

  7. #7
    Join Date
    Feb 2007
    Posts
    999
    Quote Originally Posted by beenthere View Post
    Probably do more harm then good.

    When the A/C shut off. It would have a chimney effect. And let the first floor heat rise into those rooms. making them worst then before.

    May also violate code.

    Since in a fire. The fire would be able to travel though that wall chase from the first floor to those second floor rooms even with the doors closed.
    To clarify, the stairwell grill would be at the level of the second floor, so the length between high and low grills would be about 8 feet (could be less). My comment was intended to imply that air flow out of that (stairwell) grill would flow to the downstairs grills (my guess).

    Amp

  8. #8
    Join Date
    Mar 2008
    Location
    Long Beach, CA
    Posts
    3,384
    Quote Originally Posted by ampulman View Post
    To clarify, the stairwell grill would be at the level of the second floor, so the length between high and low grills would be about 8 feet (could be less). My comment was intended to imply that air flow out of that (stairwell) grill would flow to the downstairs grills (my guess).

    Amp
    Amp,
    Are you trying to improve the performance of the AC, heater, or the fan in general?

    Overcutting the bottom of the bdrm doors to 1” will give you about 30sq inches of return per room. Using a stud bay will give you 49sq in. of return area minus the loss of 8ft of travel plus the loss of two registers grills. The two methods may be equal.

    It would boil down to whether you want the hot air on the ceiling or the cooler air on the floor to be removed from the rooms.

    As for code violations, I believe that only applies to firewalls (garages).

    And, the only air that would travel from upstairs to the downstairs returns would be the cooler air.

    Brian

  9. #9
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    4,985
    Quote Originally Posted by dash View Post
    Manual D says ,return location high or low has little effect on comfort,believe it or not.
    Right Dash, however, Manual D assumes that the duct system will be done correctly according to their standards.

    Where we have old gravity flow supply registers & very low airflow (No Throw) due to Evaporator being installed directly on top of an OIL furnace when it should be 6" above it, etc.

    We end up with cold air dropping on the floor & recirculating back through the floor returns. Room-air stratification, & very Low heatload through cooling Coil. Then, where the SA/RA grilles are located does make some difference.

    Of course, the initial mistakes should be corrected, but many don't have the money to get it done right. - Darrell

  10. #10
    Join Date
    Feb 2007
    Posts
    999
    Quote Originally Posted by Brian GC View Post
    Amp,
    Are you trying to improve the performance of the AC, heater, or the fan in general?
    Heating system is good overall; would benefit 2nd floor due to center hall (high) return and closed room doors. Ditto a/c, especially on low stage.

    Overcutting the bottom of the bdrm doors to 1” will give you about 30sq inches of return per room. Using a stud bay will give you 49sq in. of return area minus the loss of 8ft of travel plus the loss of two registers grills. The two methods may be equal.
    It would be very easy to cut 'pass-through' returns over each doorway. Would the 1" door cut lessen noise (voice) transmission as compared to the door cut? The door cut is a direct pathway (~1.5") for the sound to travel through vs. the distance between layers of sheetrock?

    [quoteIt would boil down to whether you want the hot air on the ceiling or the cooler air on the floor to be removed from the rooms.[/quote]

    The high returns in each room would preferably benefit cooling

    And, the only air that would travel from upstairs to the downstairs returns would be the cooler air.
    I'm familiar with cold air spillage from the second floor. The proposed returns (in the stairwell) would be at the level of the 2nd floor. I would think the return air would be caught in the spillage.

    Amp

  11. #11
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Quote Originally Posted by Brian GC View Post
    NOT !!!
    Ouch! That's loud. Feel better now? lol!!!

  12. #12
    Join Date
    Jan 2008
    Location
    MI
    Posts
    38
    “Manual D says, return location high or low has little effect on comfort, believe it or not.”
    Just curious: Is this part of the Manual D written on the toilet paper?