new compressor or not
i have a 5 ton trane hp (i believe XL1000). bad compressor - shorted to ground. i've never replaced just a compressor on a unit. how do i know the reversing valve is working (unit is holding good pressure - appx 150). Next question. On some old units, you can't find the same compressor i was told, so does it really matter what type of compressor as long as it is the same BTU, volts, and size? I don't want to replace compressor and unit not work?
I was told at the supply house that on these units, changing the condensors only have been burning compressors up within a year. so it seems the best solution might be to replace compressor, thanks for any helptd55
-
05-03-2009, 03:13 PM #2
Sound to me like folks aren't clean up before installing a new Comp. And /or pulling a vacume with a micron gauge to 500 microns.
JMOTHE MORE I LEARN
THE MORE I FIND I DONT KNOW
Cancer Survivor
And Dam Well
Plan On Staying That Way
-
05-03-2009, 04:01 PM #3
this should be in the technical forum
-
05-03-2009, 04:10 PM #4
Professional Member*
- Join Date
- Oct 2003
- Location
- las vegas
- Posts
- 1,505
if it is a bad burnout i would change the valve with the compressor.
usually ill get some of the oil out if the comp. & test for acid.
being a valve that shifts with pressure differential you need an operating
pump to check how it shifts. 50/50 chance it will work.
-
05-03-2009, 04:17 PM #5
Professional Member
- Join Date
- May 2008
- Posts
- 323
-