Results 1 to 13 of 29
    Mar 2009
    Toronto, Ontario
    Question Advice - AC Coil extending past plenum
    Hi,
    This week I had my new furnace and AC installed.
    I have a concern that the AC coil extends 5.5" from the plenum.
    I know that was an issue with my previous system and am having a hard time seeing how I am getting full benefit of the AC with a portion of it extended from the air flow.
    I am by no means a HVAC expert, so if this is normal and there is no impact to the system cooling efficiency then I am fine. However, if there is an impact do I need to look at a bigger plenum?
    My preference is to have the system running at it's peak and not hampered in any way.
    I'm hoping that the pros here will let me know what their recommendations are and why.
    Thanks,
    Dolfan
    garland, texas
    A picture would be most helpful.
    Fort Worth, TX
    Quote Originally Posted by nvr2old View Post
    Yes. We don't know if the OP is talking about a horizontal unit in the attic, or an upflow unit in a hall closet, or one or the other in a basement/crawl space.
    Generally speaking, it is best to not intentionally blank off a section of cooling coil, as some installations do. This is what transitions are for should the coil be larger than the air handler or furnace dimensions.
    Building Physics Rule #2:
    Building Physics Rule #3:
    Nov 2008
    Chapel Hill, NC
    Do you mean the AC coil box is wider than the plenum? If so, that's OK, you just don't want a coil box that is narrower than the plenum or furnace as that would cut air flow down significantly.
    Northeast Ohio
    Need pics
    DEM
    SW Wisconsin
    This has become a problem with the higher SEER coils & lack of room, etc. to make proper retro adjustments.
    The main thing is that the entry through the coil be open to a straight stream of airflow. Also, the drain pan, if not insulated, may sweat if out of the air stream.
    It is very important to have equal distribution of air through the coil circuits.
    Unequal distribution will result in lack of liquid evaporation which affects suction superheat.
    Due to a colder line, a TXV would tend to reduce the flow of refrigerant to the coil.
    Charging by superheat will also be OFF. Both superheat & subcooling should always be checked on all systems & compared to what they should be.
    If at all possible have the retro work done to correct any airflow problems.
    - Darrell
    Mar 2009
    Toronto, Ontario
    Will take pics tonight and post them.
    I'll try to explain it further...
    Basement install (Toronto, Canada).
    Code:
             |       |  Plenum
             |       |___
             | Coil       |
             |        ___|
             | Furnace|
    Pics will be uploaded tonight when I get home
    Nov 2008
    Chapel Hill, NC
    Hmmmm.......... It looks like the coil is offset from both the furnace and the plenum airflow and not uniformly extending out on all 4 sides. This could be a problem. Post pics!
    Mar 2009
    Toronto, Ontario
    Pictures attached
    Here are the pictures....
    Please provide your feedback.
    Thanks,
    Dolfan
    Jun 2006
    Richmond, VA
    Those should go on the wall of shame, that is not right, won't work right, words cannot describe the my shock when i saw these pics.
    I wish I had a $1.00 for every response I deleted.....
    "Decidedly Superior in a twisted pathetic way".....
    Wow. Wall of shame is right. Someone did some poor work for you there.
    Aug 2008
    Burlington , Mass
    Just when you thought you've seen everything.
    It does look as though the coil was already in that position before the new furnace was installed. and they just transitioned to it as the new furnace is shorter. Even if it was that way, the installer should have mentioned that its improper.
    You should get a new cased coil installed on the furnace ( matched to the furnace opening ). The manufacturer of the furnace will have a matching enclosed coil set up.
    I'll be there when I get there and not a minute later
    Apr 2008
    Galion, Ohio
    wow...if I did that i would be fired.....lol