    Melink Hood Exhaust System Issue

    Hi just wondering if anyone has worked with and found issues with the Melink hood system with the min VFD and low fire on the MUA. I have a few stores with this system and all my MUAs are sooting up, having issues with tripping on freeze stats, and bad inital fire offs. One store is having issues with gas smells and I am thinking it has to do with the min VFD at 75% and at low fire that I am having incomplete combustion thus the gas smell bad firing and sooting. Just wondering if anyone has ran into this, the Melink rep stats there is no problems. Thanks

  2. #2
    Join Date
    Jan 2008
    Location
    Lake Worth, FL
    Posts
    111
    Post Likes
    I have many stores with Melink. Check for clean filters, orifices on the burner and low fire gas pressure according to the specs for your model.