Page 1 of 4 1234 LastLast
Results 1 to 13 of 40
Thread: CVHF surging
    Apr 2009
    CVHF surging
    would love some input on surging on a trane cvhf. Both pressure drops match specs, no excessive pumpouts on purge, ref. level slightly high, tower water temp at 65. Also wondering if condenser approach is an indication of air in system or just fouled tubes?? Any input greatly appreciated.... just getting into chiller work thanks
    Aug 2000
    Crap shoot with the kinda info you gave. Need real information to give you a real answer. Water temp in, water temp out of both barrels, SH, SC, DSH, pressures, LL temp, type refrigerant, approaches, amperages, % of FLA, etc.
    Your poor planning does not constitute an emergency on my part!!!!
    Pacifica, California
    Both approaches should run pretty close to each other. Check your design delta T's. Make sure you have temp drop as well as pressure drop. Tubes could be fouled. Good rule of thumb is 10* @ full load. 1 degree less for every 10% short FLA.
    Go the extra mile, it's shorter than you think. UA in the Bay
    Apr 2009
    In the south
    It is usually one of three things. Air, condenser water to hot or fouled tubes. Condenser approach should be no more then 3 degrees at full load. Have you checked to see if your purge is actually working properly?
    Oct 2005
    Phoenix, Arizona
    tower water temp at 65??
    in a tree looking in your window
    Have you put an actual gauge on the machine or are you getting your "pressures" from the micro.
    If you dont stand behind our troops, please feel free...........to stand in front of them.
    socal
    No excessive pump outs ? What is your purge setting , auto, adaptive, on ,off.
    ottawa canada
    Gotta luv the newbies?????
    " Chiller's Surging" whats up wiv it ?????
    With 65 degree tower water and who knows what load maybe its a low load surge ????
    Whooo Hooo spring at last , time to get the toys out ........vrrrroooooom !!!!
    North Florida/South Georgia
    In other words
    Please post a log............
    All my leon freaked out!
    Delaware
    AS the other guys mentioned, there is not enough info in your post to arrive at a firm answer. However; if we look at the cause of " surge" perhapps you will find the cause.
    Surge happens when the impeller "stalls" (will not pump) because the differential pressures (between Evap and Cond) are greater than the designed "Lift " of the impeller. In other words the impeller cannot lift the refrigerant vapor from the evap pressure to the cond. pressure.
    Anything that is causing your machine to have a higher than normal pressure (cond) OR, a lower than normal pressure (evap) can cause surge.
    AS mentioned also, do not depend on the micro to give you correct readings. Go for the service tools (gauges and thermo's) to double check.
    Good luck and keep us posted
    Aug 2000
    A stall is not a surge. Stalling occurs before surging.
    Quote Originally Posted by Chiller Guy View Post
    Georgia
    I have a paper around here somewhere that describes what "York" put out as "rotating stall". It was primarily a low load condition that I was assured would not harm the machine. This was on a single wheel 123 chiller. It sounded like a loud grumbling sound, not a whole lot of amp fluctuation or pressure swings like you see with a "surge" surge. I'll have to dig it out of the archives, be a good excuse to go get another cold one!!!
    Georgia
    Found it, let me get it scanned in and I'll be happy to send it to those interested, it is a very good description of what is going on in a stall condition.