JCI / AX temp issues
I have a jci branded ax jace with about 40 devices on the n2 bus and some of the vma's for the fan powered boxes get wild readings on the space temps (109 deg. etc.) when the room is 70 deg. and they return to normal on there own, any ideas ?
-
03-31-2009, 06:21 PM #2
Professional Member*
- Join Date
- Mar 2009
- Location
- Several Miles from Sane
- Posts
- 1,401
Which model ? If it's an FX-20 you have bigger problems than you think. If it's an FX-40 or 60 you're o.k.
Try looking at the VMA's via HVAC-Pro (either via T-stat or direct on N2 bus, disconnect the FX first) and look for the COS values on the AI's, specifically Zone Temp, Remote Setpoint/Adjust and the Velocity input. If they are less than 1.0 change them to 1.0 or more. If that doesn't help try reducing your individual point count for each VMA to less than 12.
If you're working with a 20 JC recommends total devices less than 35, total points less than 350. My only suggestion would be to drop the point count on each VMA to absolute minimum (6 each is about as low as you dare go) and cross your fingers. Only other option is to replace with a 40 or 60 (60 prefered).
good luck if it's a 20 !If sense were so common everyone would have it !
All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!
-
03-31-2009, 07:02 PM #3
Banned
- Join Date
- Mar 2006
- Posts
- 3,641
-
03-31-2009, 11:32 PM #4
Professional Member*
- Join Date
- Mar 2009
- Location
- Several Miles from Sane
- Posts
- 1,401
If sense were so common everyone would have it !
All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!
-
04-01-2009, 04:08 PM #5
Regular Guest
- Join Date
- Apr 2004
- Posts
- 566
I went back today,hvac pro = 8.08, and i changed the cov setting from.5 to 1.0 on a couple boxes and they worked normal,but the problem may have been that the stat/n2 wires were run across the trigger board for the heat scr's, i'll post the results later
Thanks
By the way do i have to have workbench software to tell what jar file the n2 is ? i'm working from the embedded software in the fx40.
-
04-01-2009, 06:55 PM #6
Professional Member*
- Join Date
- Mar 2009
- Location
- Several Miles from Sane
- Posts
- 1,401
I went diggin in a Rev 2.0 via the browser. I can't figure out a way to see them. I am afraid you do need FX-Workbench. Freddy-b may have more info but I can't ever remember being able to get to the *.jar file without WB.
If sense were so common everyone would have it !
All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!
-
04-01-2009, 07:39 PM #7
-
04-02-2009, 06:19 PM #8
Regular Guest
- Join Date
- Apr 2004
- Posts
- 566
Thanks i'll post the results later.


Reply With Quote