How do you measure the pressure in the condenser when it's pumped down? Yesterday I checked for noncondensables by running the condenser fan, but I didn't pump the system down. (High subcooling high superheat, TXV coil.) I got a perfect match between ambient and SDT, so no noncondensables. Determined it was a restriction, like I first suspected. Then to track down the restriction I dropped subcooling at the liquid line service valve to 1 deg by reducing system charge and bypassing LP switch, then measured liquid line temp drop from the service valve to the TXV inlet. 5 deg total drop. This means that the liquid line, including the filter dryer, was using up only 6 degrees of subcooling. Not the problem. Determined that it has a bad TXV (no inlet screen). TXV to be replaced Monday.
-