Thread: Larkin freezer

  1. #14
    Join Date
    Jan 2005
    Location
    Veterans Home Yaphank, NY
    Posts
    2,309
    Had a nursing home with a walk-in like that. The thermostat was in series with the coil of the compressor contactor. When satisfied it would break the line to the coil, compressor would shut off. However there is no pumpdown with this method, so the compressor can try and start against a full load.
    This is a good cause of "flooded start" which can damage the compressor. The late Glen Henigan from Copeland did an excellent video about this.
    Next time back, explain this to the customer as this is a Compressor Killer.
    RAM Teaching Tomorrows Technicians Today.

  2. #15
    Join Date
    Mar 2008
    Location
    20141
    Posts
    1,153
    I can tell you this guy wouldn't have given a $#!t anyway. I've got a bunch of numbers off of the comp. I think it was an "AH" series. It's in the trucl I'll try n post when I get home from class.
    I am the Stig

  3. #16
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,379
    When the customer starts telling me "no", I just repeat it back to them. "no" I will not warranty the work, or do the work without doing x,y and z.

  4. #17
    Join Date
    Mar 2009
    Location
    central illinois
    Posts
    532
    do what you got to do to get it up and running if owner to cheap to make it right put it on ticket make sure it is signed cya. if i walked away from a job because he would not let me do it the right way my boss would have a cow.excluding dangerous situations.
    work to live not live to work.

  5. #18
    Join Date
    Nov 2000
    Location
    Memphis TN USA
    Posts
    6,945
    First off small boxes should have the gas weighed in. You might have to add a little after that if the system has other problems.

    Now why did the first tech get a call on that box? Something was wrong. I have seen them cycle on thermal when they run in a vacuum. A tech might condemn a compressor that was out on thermal. I would suspect the worst and at least write something on the ticket that says the owner did not want the box repaired, just wanted it to run.
    If the superheat ain't right it ain't charged right.

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event