    questions about a heat pump issue

    Hello,
    I have a new system that was installed just a few months ago. It’s an American Standard Freedom 95 Comfort-R forced hot air. Two stages of gas fired heat (highest is 60k BTU), one stage heat-pump / cooling 1.5 ton I think, 16 SEER.

    Everything on this system works great except for a bit of an issue with the heat pump. When I purchased the system there was a claim that it could (efficiently) work all the way down to 25F. I thought this was ambitious but some of this modern stuff is pretty good. Well, turns out that it could not really do this. The system would stay on and would run indefinitely (using electricity) and only get up to maybe 60F or 65F when set to 70F.

    OK, so the company came out and made some adjustments, checked for problems, refrigerant, and notably changed the crossover point to 35F. No-go, same result. They came out again and changed a few more settings (in the thermostat) but kept the 35F set point. Still mostly a problem, it worked great while they were here and the outside temp was 37F, but later that week it would sometimes work, sometimes not. Even one time I noticed it took 3 hours to get up to 67F when the outside temp was 48F, other days it might be faster or slower around the same temperatures.

    They walked me through changing the set point to 40F, and this made things a little better, but still somewhat inconsistent. For reference, when on gas it can get the place up to 70F from 62F in less than 20 minutes. It’s a 1400 Sq. Ft. Condo in Boston. At my request, they did contact the manufacturer representative for an expert opinion but they said setting it to 40F was about all you could do, and they did not think it was any defect in the unit. They also said that even when within the temperature range needed, the unit can be affected by weather conditions like rain, sun, and wind. The condenser is located in a narrow alley outside my building, and right next to it is another condenser that I have for a Mitsubishi Mr. Slim 22 SEER heat pump that says it will work down to 15F and works great down to 5F!!!

    My questions on this are, are these acceptable results? It only cost a little bit more to add the heat pump over the non-heat pump unit, and I had to pay some high electric bills during these trials, but with a set point of 40F the heat pump is only going to be working for a few months out of the year, and what about this inconsistent performance? Should I be expecting more? Could this unit be defective? Are there other units that COULD work down to 25F for a whole-house unit like this? American Standard only has one unit above this, with I think 19 SEER using a two-stage condense that is even larger than the gigantic one that I got. But it was a huge step up in price and would not have paid for itself anytime soon. I would like to hear from some other experts about this situation.







    This leads me to another separate question I have about this. Does anyone know of some really powerful computer-controlled thermostats? The one that came with this system is pretty nice, but obviously it is not nice enough to detect that the heat pump isn’t cutting it and will keep running endlessly never reaching the temperature instead of switching fuels. I have seen there are some “Ethernet equipped” thermostats you can connect to your home network that provide a web management page, but looks like they otherwise have the same features as what I have.

    I am talking about something REALLY computer controlled, like a piece of software. Something that would have more sensors and could detect which fuel to use based on actual output/consumption over time even being able to compensate in real time for weather or other conditions. Advanced energy management features that would get the most out of the multiple stages, variable speed fan, etc. I will bet there are some home automation products that might have this, but I thought I might ask if someone knows of anything that might be exactly what I am looking for.

    Thanks very much in advance

    Jcl333

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,793
    The heat pump will "work" at the low temps they claimed.
    It just won't be able to supply enough heat to maintain temp.

    Your heat ump is sized to your cooling load, not your heating load, which is proper.

    A thermostat like the Honeywell IAQ can be set up to use the HP first, and if it can't keep up. It will switch to the furnace.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Apr 2008
    Location
    Galion, Ohio
    Posts
    83

    well

    Sounds to me like they either have some wiring issues, or thermostat settings, that are screwy.

    There are so many things though, that it would be hard to diagnose over the net. Could be inproper charge...all kinds of things

    Should not have to raise your lockout temp to get things to work...a good stat will monitor the heat pump running and if it cant keep up, should kick in a second stage of heat....being furnace, elec heat, or whatever.

  4. #4
    Join Date
    Jun 2007
    Location
    The Twilight Zone
    Posts
    2,964
    Your heat pump is only 1.5 tons, the smallest size in a split system. As BeenThere stated, it is sized for the cooling load and not the heating load. Your gas furnace provides supplimental heating when the heat pump cannot provide enough btu's. As outdoor temps drop, so does the btu output of the heat pump. It may provide 18,000 btu's (1.5 tons) at 47F (the outdoor rating temp), but only 12,000 btu at 25F ambient.

    Take care.

  5. #5
    Join Date
    Sep 2005
    Location
    Bay Area, CA
    Posts
    843
    The 16 seers are trick to install, they dont come in 1.5 tons though to my knowledge they only do even tonage. Usually the issue is with new installs is control wiring and fan settings.
    Global Warming or: None like it hot
    No pleasure, no rapture, no exquisite sin greater... than central air. -Dogma

  6. #6
    Join Date
    Mar 2009
    Posts
    12
    I think another question would be how involved with heat pumps is the installing contractor. It's a growing segment of the business here in Chicago because gas and electric pricing made it an extremely inefficient choice until recently. Going through the training myself, I learned that ,at least in the Lennox units, very often you will not use the same coil for heat pump as for a/c. You need more coil volume for heat pump mode. If you don't have the correct coil or TXV matchup you would have a heating issue with the heat pump.

  7. #7
    Join Date
    Apr 2008
    Location
    Galion, Ohio
    Posts
    83
    I agree with green jumper.

    The 16i does have to be wired differently, have the install manuals in my van, forget exactly what the "combination" is. But know they are wired a little different on the low volt side.

    I would contact the company who put it in with these ideas in mind.

    If you follow wiring directions supplied with the O/D unit, it will run correctly....wiring schem for stat/furn shows it a little differently.

  8. #8
    Join Date
    Apr 2008
    Location
    Galion, Ohio
    Posts
    83
    Actually, trane 800 series stat book has a 16i wiring configuration...now that I think of it.

  9. #9
    Join Date
    Aug 2007
    Location
    Okmulgee, OK
    Posts
    184
    Strange part is that you say sometimes it works good, sometimes it don't. It's also strange that the stat is not bringing on the gas furnace when the heat pump is not keeping up. I agree 100% that you may have more than one problem.

  10. #10
    Join Date
    Jan 2008
    Location
    Somerville, MA
    Posts
    23
    Quote Originally Posted by beenthere View Post
    The heat pump will "work" at the low temps they claimed.
    It just won't be able to supply enough heat to maintain temp.

    Your heat ump is sized to your cooling load, not your heating load, which is proper.

    Well, I am getting ready to upgrade my insulation, maybe after that it will be able to do this.

    A thermostat like the Honeywell IAQ can be set up to use the HP first, and if it can't keep up. It will switch to the furnace.
    Hey, this is a great (and interesting) tip! I went to the Honeywell website to look at this thermometer, and it looks identical to the one I have except mine does not have the other white box, and my says "American Standard" instead of Honeywell. Yeah, I know my system is made by Honeywell.

    My currect thermostat says "ACONT802AS32DAA" and "TH8320U1032" on the back. Are you thinking that the thermostat that I have does not have the feature to detect that the heat output is not enough and switch, whereas this higher end model you are mentioning can?

    If that is the case, I will call my HVAC company and have them install one of these units. I already have Aprilaire filtration and humidification, but auto-switching fuels would probably be worth it.

    What do you think?

    And thanks

    JCL333

  11. #11
    Join Date
    Jan 2008
    Location
    Somerville, MA
    Posts
    23
    Quote Originally Posted by brianalan01 View Post
    Sounds to me like they either have some wiring issues, or thermostat settings, that are screwy.

    There are so many things though, that it would be hard to diagnose over the net. Could be inproper charge...all kinds of things

    Well, do you think my situation warrants hiring a different contractor to get a second opinion? If so, I think it might be hard to filter contractors in the area for the the real "heat pump guru"...

    Should not have to raise your lockout temp to get things to work...a good stat will monitor the heat pump running and if it cant keep up, should kick in a second stage of heat....being furnace, elec heat, or whatever.
    I agree with you, but that is not what is happening. This thermostat will do "recovery" such that it starts working early enough so that it reaches set temp by the time you have set instead of starting at that time. But, on days I have been home all day it starts at like 3:00pm to "recover" to the temperature it needs to be at by 5:30pm. Seems like a long time to me.

    -JCL333

  12. #12
    Join Date
    Jan 2008
    Location
    Somerville, MA
    Posts
    23
    Quote Originally Posted by gary_g View Post
    Your heat pump is only 1.5 tons, the smallest size in a split system. As BeenThere stated, it is sized for the cooling load and not the heating load. Your gas furnace provides supplimental heating when the heat pump cannot provide enough btu's. As outdoor temps drop, so does the btu output of the heat pump. It may provide 18,000 btu's (1.5 tons) at 47F (the outdoor rating temp), but only 12,000 btu at 25F ambient.

    Take care.
    So, you are basically saying it "is what it is" and if I want this to work for a longer part of the year then I would have to improve my insulation?

    My cooling load in the summer is very low, I am on the first floor of a 4-story building that is steel and concrete.

    But, if I understand you correctly, if it is sized for the cooling load, then how often the heat pump gets used is entirely based on the heat loss of the particular dwelling. Because I imagine if you sized the unit for heating, it would be way oversized for cooling.

    -JCL333

  13. #13
    Join Date
    Jan 2004
    Location
    PA
    Posts
    68,793
    The IAQ has a better control logic.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 1 of 6 123456 LastLast

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event