What size Hvac Unit
Just received a quote on a new system on a new home were building. HVAC Contarctor did a J manual Calculation and said it could be a 3 or 3
1/2 ton unit. Don,t want to oversize. Here are the results, what are you thoughts?
AREA 1878
Sen Gain 35,186
Lat Gain 4,371
Net Gain 39,557
Sen Loss 92,875
Sys Htg CFM 1,161
Sys Clg CFM 1,549
Sys Act CFM 1,549
Duct Size 22x12
-
03-24-2009, 01:54 PM #2
What were the design conditions.
-
03-24-2009, 02:14 PM #3
Professional Member
- Join Date
- Nov 2008
- Location
- Biloxi, Ms.
- Posts
- 174
I can't get that much sensible out of any 3 or 3 1/2 ton system that we sell.