    Amprobe TMULD-300

    Anyone use this leak detetctor and like it? Amprobe It says it has a transmitter that puts a signal in the lineset that the reciever picks up through a leak. Hows that work?
    Eat a slice of Humble Pie.

  2. #2
    Join Date
    Dec 2005
    Posts
    7,904
    Post Likes
    Every now and again someone mentions these leak detectors, usually its in a thread about leak detectors. From what I've read and heard some people find them useful. They can be tough to use in noisy environments. Theres been one or two guys that swear by that particular model you linked. But like everything else there are many that say they don't work too good and swear at em.

  3. #3
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes
    Quote Originally Posted by rogerk View Post
    Hows that work?
    From your link, it seems like leaks generate noise at freqs. above the human range of hearing (20 Hz to 18 kHz). This thing, and probably any dog, can hear the noise that the leak makes from the air escaping.
    http://www.google.com/search?client=...UTF-8&oe=UTF-8

    It's clever, if it actually works and doesn't give false indications.

    So I guess the hissing noise from air leaking from a tire also has frequencies way above what we can hear.

    http://www.google.com/search?client=...UTF-8&oe=UTF-8

  4. #4
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by rogerk View Post
    Anyone use this leak detetctor and like it? Amprobe It says it has a transmitter that puts a signal in the lineset that the reciever picks up through a leak. Hows that work?
    Where did you read that it puts a signal in the lineset?

    I was just looking into the Inficon Whisper ultrasonic leak detector. A friend at the supply house is ordering in one for the store and he's going to let me check it out to see how I like it. I can't find any extensive reviews on the thing anywhere. My experience will have to be the review that I ultimately base my decision on. I have a few tests lined up for it. If it passes them, then I'll buy it. One of the reasons I'm considering an ultrasonic is to check for vacuum leaks around hose fittings etc when I'm pulling a vacuum. That will be the first test that I run on it. I have a couple older hoses and manifolds that I know will leak. AFAIK there is no other type of leak detector that can pick up vacuum leaks.

  5. #5
    Join Date
    Dec 2002
    Location
    Tampa, Florida
    Posts
    706
    Post Likes

    Talking I swear by it...

    I am 1 of the 2 guys that swear by it as "NewOldTech" mentioned previously. Roger, how is that HVAC SUPERTECH program working for you? I hope it has been useful! The Amprobe TMULD-300, I believe, is the best ultra-sonic leak detector on the market. I have either purchased, borrowed or tested just about all of the ultra-sonic leak detectors and in my opinion, all of them suck when compared to the Amprobe TMULD-300.

    Here are some of the features that I like about it:
    1. small and compact it fits easily in my front pocket, headphones around the neck
    2. it operates on a 9 VDC battery, I replace my battery for the first time about four years after purchasing.
    3. Very easy and simple to use. Once you know what a leak sounds like, it is unmistakable you will not forget it. The sound of a leak sounds similar to the wind noise you would hear when speaking to someone on a cell phone on a windy day.
    4. No false-positive readings, once you know what you're listening for. After identifying a leak doublecheck using soap bubbles to confirm.
    5. Unlike sniffer detectors, you do not have to hover over the leak for 3 to 5 seconds in order for it to register.
    6. Can be used in mechanical rooms by using the parabolic attachment and turning the sensitivity down a bit.
    7. The sound generator can be used in many ways. Last time I used it was on a commercial reach-in refrigerator. The bottom of the door gasket was leaking. Customer just replace the door gasket himself, and was quite sure that it was not leaking. Place the sound generator in the box, closed-door. Using the detector, I went around the perimeter of the door and when I got to the bottom of the door, near the center, the detector proved to the owner that the gasket was indeed leaking.
    8. I believe you can get the detector for less than $200 on eBay or similar auction sites. Compare this to a sniffer detector, a good one starts at $300 and up.
    9. Most importantly, it can be used on any refrigerant or gases under pressure. I have found leaks in systems using as little as 20 to 30 psi pressure
    Here's some of the other ways that I used to detector, other than for HVAC. You can use it to check bearings in a motor while running, finding small pinhole leaks in an air mattress caused by the cat, checking truck tires for leaks and water leaks behind drywall.

    Roger, this is an exceptional tool to have in your arsenal for detecting refrigerant leaks. Once you begin using it and get familiar with it -your other leak detectors will most likely stay on the truck shelf until a time comes where it is not feasible to use the ultrasonic detector. I have written about this particular leak detector a few times, search my postings to find them. I would not steer you wrong, these detectors are truly awesome!

  6. #6
    Join Date
    Oct 2007
    Location
    ATLANTA
    Posts
    121
    Post Likes
    Quote Originally Posted by rogerk View Post
    Anyone use this leak detetctor and like it? Amprobe It says it has a transmitter that puts a signal in the lineset that the reciever picks up through a leak. Hows that work?

    Hi

    I once was misled by the ultrasonic transmitter. I also thought that it could send sound signals into a line set. By the way some of the literature reads.It indicates that the transmitter can be used for leak testing a non pressurized system.

    THIS IS NOT THE CASE AT ALL!!!!
    The transmitter WILL NOT and CAN NOT send ultrasonic frequency into a refrigerant circuit or a line set.

    What the transmitter can do is generate a detectable signal when you place it inside a deep freezer for example and close the lid the signal is detected where there are leaks in the freezers door gasket etc.
    The literature also shows placing the transmitter in an attic and then use the detector from the roof top to help locate a roof leak as well as some other ideas for its use.

    As far as the detector itself I have used one for around a year now and have had some phenominal results at finding leaks with it when other methods did not work very well. Such as where I used it in a large walk in cooler evaporator in a large chain grocery store.
    The leak was about 5 inches deep in the center of the coil and soap bubbles did not work as that the bubbles disipated before they could become visible,pressurizing with Nitrogen did not help because you could not hear a hiss with the naked ear and sniffer leak detectors all went crazy when you got within 5 feet of the coil even with good discrimination features.
    So locating exactly where the leak was had perplexed 2 other technicians and all quoted entire new evaporator coil replacements.

    With the ultrasonic detector I was able to pin point where the leak was within around a 2 to 3 inch radius and cut back the fins in that area and went straight to the leak and repaired it.
    I worked this same magic on a large walk in freezer and in a beer cooler all of which other service companies had reported that entire coil replacement was the only option to the customer.

    Needless to say I became an instant hero and the national facilities manager was so impressed that we soon took over the contract as the outside service provider for this large grocery store chain.

    However I have used the Ultrasonic detector on some leak searches where it did not work at all. You see the leak has to be producing a detectable ultrasonic sound and NOT ALL LEAKS will produce a detectable sound.Plus I have found that some fluorescent lights and other equipment can give off frequencies that can hinder the Ultrasonics use in some environments.

    Regardless of the short comings I now carry the Ultrasonic with me on ALL leak searches because it has proven itself as a cutting edge tool that can help find leaks when other detection systems fail.Especially good results on roof top package units and outside condensers where the air movement from breezes can make using a sniffer type detector as useless.

    Best Regards
    Lee Adams
    Last edited by AtoZhvac; 03-22-2009 at 01:27 AM. Reason: added texts

  7. #7
    Join Date
    Aug 2004
    Location
    Wpg Mb Canada.
    Posts
    338
    Post Likes
    Sounds like an interesting concept. It is probably worth pointing out that your not going to detect a leak with ultra sonic by running the business end of the detector down along some honeycomb grills in an operating supermarket or things of this nature.
    I think the sniffer is a good option to check for leaks broadly and quickly, and the ultrasonic would work efficiently at pin pointing leaks.

    And the transmitter/detector duo.
    For roof or sound proofing a house I can see use, but in refrigeration, for checking box leaks, you wont find anything better than a lighter to accomplish this.
    gahh

  8. #8
    Join Date
    Oct 2007
    Location
    ATLANTA
    Posts
    121
    Post Likes
    Quote Originally Posted by skr0oface View Post
    Sounds like an interesting concept. It is probably worth pointing out that your not going to detect a leak with ultra sonic by running the business end of the detector down along some honeycomb grills in an operating supermarket or things of this nature.
    I think the sniffer is a good option to check for leaks broadly and quickly, and the ultrasonic would work efficiently at pin pointing leaks.

    And the transmitter/detector duo.
    For roof or sound proofing a house I can see use, but in refrigeration, for checking box leaks, you wont find anything better than a lighter to accomplish this.

    Actually in my experiences with the Ultrasonic detector when a leak is creating a detectable ultrasonic sound the detector in some cases can pick up the leak sound from a fairly long distance away even up to a couple of feet or more without removing all of the cover panels etc.Although it best of course if you can get as close to the coil or tubing as possible.
    Even though the literature with the Amprobe detector states that leak sounds are directional in their nature I have actually detected leaks spewing in the opposite direction with good clarity 8 to 10 inches away!

    Once familiar with its operation leak scans can be done pretty fast in fact the Ultrasonic detector is the very first piece of equipment that I start my leak searches with. I can quickly determine if the leak is giving off a detectable ultrasonic sound and if not then I will use the sniffer and bubble methods as double verification. This has saved me lots of time on leak searches by having all of these resources available.

    The Amprobe Ultrasonic leak detector for me is right up there with the VETO PRO PAC as one of those tools thats guaranteed to make you feel good
    Last edited by AtoZhvac; 03-22-2009 at 02:16 PM.

  9. #9
    Join Date
    Mar 2006
    Location
    DFW
    Posts
    3,967
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacrmedic View Post
    Where did you read that it puts a signal in the lineset?
    Maybe I was misled. I read an add in RSES March 2009 issue pg. 18. "The TMULD-300 version includes a seperate transmitter to inject an area with ultrasonic sound to pinpoint leaks without the need to pressurize a system - perfect during repairs - as there is no need to re-pressurize a system to determine if all leaks were repaired." Reading this makes it sound like there is a way to connect the transmitter to the lineset and somehow send the sound produced by the transmitter into the lineset. I think amprobe should reword their add as it is very misleading IMO.
    Eat a slice of Humble Pie.

  10. #10
    Join Date
    Mar 2006
    Location
    DFW
    Posts
    3,967
    Post Likes
    Thread Starter
    Quote Originally Posted by badbillr View Post
    Roger, this is an exceptional tool to have in your arsenal for detecting refrigerant leaks. Once you begin using it and get familiar with it -your other leak detectors will most likely stay on the truck shelf until a time comes where it is not feasible to use the ultrasonic detector. I have written about this particular leak detector a few times, search my postings to find them. I would not steer you wrong, these detectors are truly awesome!
    Ordered 1 today for $300.00. Hopefully it will work better than my sniffers have.
    Eat a slice of Humble Pie.

  11. #11
    Join Date
    Dec 2005
    Posts
    7,904
    Post Likes
    Quote Originally Posted by rogerk View Post
    Ordered 1 today for $300.00. Hopefully it will work better than my sniffers have.
    Sweet!

    I've almost pulled the trigger a couple of times but came up short. After getting some feedback from the forum I recently purchased a Dye kit. I used it once and was VERY pleased with the results.

    After you get and use your ultrasound gives us the facts.

  12. #12
    Join Date
    Mar 2006
    Location
    DFW
    Posts
    3,967
    Post Likes
    Thread Starter
    Quote Originally Posted by newoldtech View Post
    After you get and use your ultrasound gives us the facts.
    You can count on that.
    Eat a slice of Humble Pie.

  13. #13
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes

    This Amprobe thing uses 40 kHz

    and the wavelength of sound at 40 kHz is 1/3rd (~5/16ths) of an inch.

    Can anyone confirm that this thing is better at detecting holes bigger than 5/16ths of an inch and not good at finding holes 1/16th and smaller?
    Is it better at finding round holes than at finding slots?

    From your posts, I think now all it does is shift the 40 kHz down to something audible, like 5 or 10 kHz.

    Thanks.

  14. #14
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by rogerk View Post
    Ordered 1 today for $300.00. Hopefully it will work better than my sniffers have.
    I've also got one on the way. 301.99 plus shipping for the TMULD-300. Thanks for bringing the Amprobe to my attention. I was about to waste money on the Inficon version. The Inficon doesn't let you "hear" the leak, it just clicks the same way the D-tek does. I'd rather hear what I'm listening to rather than hearing an artificially generated click. I'm thinking the Amprobe will allow better discrimination between noise sources. It's also much smaller, better to get into tight places with.
    Last edited by hvacrmedic; 03-22-2009 at 11:28 PM.

  15. #15
    Join Date
    Oct 2007
    Location
    ATLANTA
    Posts
    121
    Post Likes
    Quote Originally Posted by WhoIsThat? View Post
    and the wavelength of sound at 40 kHz is 1/3rd (~5/16ths) of an inch.

    Can anyone confirm that this thing is better at detecting holes bigger than 5/16ths of an inch and not good at finding holes 1/16th and smaller?
    Is it better at finding round holes than at finding slots?

    From your posts, I think now all it does is shift the 40 kHz down to something audible, like 5 or 10 kHz.

    Thanks.

    I have detected leak holes as small as the diameter size of the tip of a sewing needle with the ultrasonic detector.I suspect that certain shapes of leaks could be more likely to give off a detectable ultrasonic sound.
    As I mentioned in a previous post there are some leaks that the ultrasonic will not detect when there is not sufficient ultrasonic sound being emitted. An example from my personal experience is a leak that was under a flare cap on an expansion valve was not detectable.

    Best Regards
    Lee Adams

  16. #16
    Join Date
    Nov 2008
    Posts
    1,673
    Post Likes
    Quote Originally Posted by Lee Adams View Post
    I have detected leak holes as small as the diameter size of the tip of a sewing needle with the ultrasonic detector.I suspect that certain shapes of leaks could be more likely to give off a detectable ultrasonic sound.
    As I mentioned in a previous post there are some leaks that the ultrasonic will not detect when there is not sufficient ultrasonic sound being emitted. An example from my personal experience is a leak that was under a flare cap on an expansion valve was not detectable.

    Best Regards
    Lee Adams
    Thanks.

    Now that we're talking about this, I agree that it is better to "hear" the leak. That way all the sophistication of the ear/brain connection can be used, and an experienced listener can probably get pretty good at finding leaks.

  17. #17
    Join Date
    Mar 2006
    Location
    DFW
    Posts
    3,967
    Post Likes
    Thread Starter
    I have used it on about 5 units so far and can only say what a piece of junk. You get alot of wind noise outside trying to find a leak at the condenser and even with the hose attachment its hard to reach alot of the evap coil. I plan on selling it on ebay. What a waste of $$$.
    Eat a slice of Humble Pie.

  18. #18
    Join Date
    Mar 2008
    Location
    Fuquay Varina, N.C.
    Posts
    1,053
    Post Likes
    Let me know when you do, I may be interested in bidding on it. unless you would like to offer me a reasonable price to try it for myself.
    RSES Member.
    Mainstream Engineering Certified.
    HVAC/R PM Technician.
    410A, & GREEN HVAC/R Technician.
    Indoor Air Quality Master Technician.
    NATE Core.
    Working not as to please men but to the Glory of Christ my KING.

  19. #19
    Join Date
    Jul 2000
    Location
    NW IL.
    Posts
    3,942
    Post Likes
    In the USAF we used Delvan Ultrasonics. Earphones, air probe, and ground probe. Adjustable sensitivity and adjustable volume. Delvan is no longer available, sigh.

    Most ultrasonics available to us only control either volume or sensitivity. But don't despair for most applications they will do quite well.

    Today received the Accutrak VPE-1000. Has a Koss stereo headset with a monotone/stereo switch, a touch probe attachment, and air probe attachment. Has volume control and a sensitivity control. The probe can be adjusted for one sensitivity and the air sensitivity can be set at a different setting. It has a led display for the recording. This can be set by the mode switch to display continuous or peak hold. In continuous it displays the sound in real time in peak hold it will hold the highest level for 5 seconds.

    Now I have a GoPro150 and a Amprobe ULD100 ultrasonics but just wanted something better. Well dug out that leaking solenoid stem for the upcoming seminar. Even with 200 psi the leak is more of a seep than a true leak. Neither 3 picked the seep up. Just not enough air disturbance. Covered the area with soap solution and even though the leak is visible the GoPro and the Amprobe barely moved one blip in the display window. The VPE-1000? Well it sounded like an M-16 in auto select going off in the headset. The LEDs displayed one quarter of the way up the window.

    Recommendation.......... If you are going to get an ultrasonic research carefully what you are going to buy. The VPE-1000 costs around a $1,000, but with the test I just did at home with 3 ultrasonics the VPE-1000 looks like it is a very good ultrasonic.
    Aircraft Mechanical Accessories Technician. The Air Force changed the job title to Air Craft Environmental Systems Technician. But I've decided I'll always be a Mech Acc.

  20. #20
    Join Date
    Oct 2007
    Location
    NJ
    Posts
    610
    Post Likes
    I was about to pick up the Infacon D-Tec Select Infrared b/c its on sale at Johnstone, but now im going to pick one of the Amprobe units up.

    What on-line store carries them?

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •