    Trane AH541

    I am trying to reset all AH541's after a fire alarm. The site has some version #1 and some version #2. I first used CPL to shutdown all AHU's when there was a fire alarm. The problem is with the verson #2 AH541's. They lock out on airflow before the CPL shuts down the AHU. Does anyone have a good CPL program to reset all the AH541's after a fire alarm?

    Thanks

  2. #2
    Join Date
    Jun 2004
    Posts
    727
    I believe you can make BO's and reference them to the alarm reset point in the ah541, then just have your cpl toggle that point after the fire alarm goes away.

  3. #3
    Join Date
    Jun 2008
    Location
    British Columbia Canada
    Posts
    27
    I will be on site next week and try a few ideas, including yours. Thanks