    Refrigeration and Air Conditioning Technology by Whitman instructs you to perform a standing pressure test by filling a new system with dry nitrogen up to the operating pressure of the system. It does not instruct you to pull a vacuum first before introducing the nitrogen.
    Do you first pull a vacuum to remove any moisture or non-condensables?
    Pull the vacuum after the leak test.
    Also if you're just testing the your field welds, bubbles and or a good sniffer is you're best bet.
    Grottoes VA
    Quote Originally Posted by mls228 View Post
    You should already be flowing n2 while your brazing, right?
    Jun 2008
    Quote Originally Posted by karsthuntr View Post
    Yes, absolutely.
    then Tripple evac.
    Jul 2001
    Standing pressure test to check for leaks. If no leaks, blow nitrogen, evacuate and charge system. If there is a leak, repair it, pressure check again with nitrogen, then follow procedures. If you have a leak in a system, why would you try and pull a vacuum first and run the chance of drawing air, moisture etc into the system? Find the leaks, fix them then do you evacuation and charge.
    Anytown USA
    i usually dump a little refrigerant in the system then pump it up with nitro to 200-250psi. go around with the leak detector , if no leaks dump that nitro, pull a vacuum and charge.
    I never pull a vacuum on a known leaking system. In my thinking, a new system is a leaking system until you prove it isnt.
    Mar 2009
    Colonie, NY
    on an install if u time it right pressure testing is just in time for lunch. ramp up the nitrogen to 200psig then go get lunch if its still 200 when u get bck dump that evacuate and charge.