    Help with low ambient kit

    Deadlines are coming up and this low ambient kit is driving me crazy.

    I found the pdf file online that I have in my hands but something doesn't look right.

    Coming off the transformer are six wires with spade stake ons that are all supposed to come together and go to terminal #2?

    If that was the case I can't figure out why they wouldn't have wired it factory in this configuration.

    The bottom diagram is the one I need (two fan).

    L1+L2 coming off the contactor to tb in the diagram - Check, looks alright
    red,yel,blu,org,tan,bl/wh all coming together and going to terminal 2?



    The york controls guy is out of town until next tuesday and we're off to build a walk in.

    Does this diagram look correct to any of you?

    http://www.luxaire.com/PDFFiles/102692-UAI-A-1004.pdf

  2. #2
    Join Date
    Nov 2007
    Posts
    24
    You only connect one of the six transformer terminals based on your line voltage. Refer to table 1

  3. #3
    Join Date
    Jul 2008
    Location
    Nova-Scotia, Canada
    Posts
    271
    Now it's making more sense. Reading helps once in a while.

    I'm sold on tan I believe since it's a 575v unit I'll check nameplate to verify.

    Great news. Thanks a bunch. Armament lives another day without frying expensive equipment

    I wonder why there's so many other wiring options not listed?