    heat pump amps

    i have goodman SSZ14 Heat Pump. im wanting to know how many amps it pull when it is heating and cooling. it looks like to me from goodmans website it uses 10 to 15 amps but that dont seem right it is on a 30 amp breaker. im just trying to see how it cost me to run it for an hour.

  2. #2
    Join Date
    Sep 2002
    Location
    I don't know
    Posts
    2,903
    The breaker is just there to protect the circuit.

    10 to 15 amps sounds about right for 2-3.5 ton units. Actual amp draw varies depending on operating conditions.

    Goodman has all the data available in their spec sheets.
    General public's attitude towards our energy predicament: "I reject the reality of finite resource depletion and substitute it with my own; energy is infinite, we just need an alternative storage medium to run the cars on. The economy can grow indefinitely - we just need to "green" everything! Technology is energy! Peak what?"

  3. #3
    Join Date
    Jun 2007
    Location
    louisville ky
    Posts
    107
    it is a 3 ton

  4. #4
    Join Date
    Mar 2009
    Location
    Candia, NH
    Posts
    44
    The compressor draws higher amps on start-up then it does during normal operation, hence the 30 amp breaker. Use Ohm's Law to figure out your amp draw.

  5. #5
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,712
    30 amp is the max amp protection it is allowed to be connected to.
    And 22.4 the minimum.

    The actual amp draw will vary as the load it is working against varies.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  6. #6
    Join Date
    Jun 2007
    Location
    louisville ky
    Posts
    107
    i was asking because i had a friend over the other day and he saw my breaker box is only 100 amps. i have electric stove, water heater, dryer and heatpump (with gas furnace backup). he said that was way to much for a 100 amp service. is that true?

  7. #7
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,712
    Your at the limits of your electrical service.

    How often do you intend to being using all four burners of your range, running your dryer, tapping large amounts of hot water, and running your HP in cooling mode at all at the same time while its 95 plus degrees outside.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  8. #8
    Join Date
    Nov 2004
    Location
    South Carolina
    Posts
    1,840
    you m ake a good point been, most people just add them up and freak when it is more than the system- they don't realize that not all of the stuff is on at the same time- hence- call a professional

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event