Results 1 to 8 of 8
    Charging a heat pump with big outdoor but small indoor coils
    Hi everyone. Nice to find this forum. I recently have problem charging a heat pump that has a relatively small indoor coil. I charged the unit per rating plate using the subcooling method in cooling mode. For some reasons, the subcooling is not very sensitive to the charge. I had to add 2 lbm to increase 2 °F subcooling!!! I ended up adding lots of charge to the system to get to the rating plate pressure. The unit seemed working fine in cooling mode. However, when the unit switched to heating mode, I noticed a significant high head pressure, like 550 pisg at 47 ambient. I removed lots of refrigerant out to get the pressure below 400 psig.
    I am thinking the problem is the indoor coil is too small for this outdoor unit. Does anyone know of any other way to charge this kind of system?
    Lancaster PA
    let me guess.
    You installed a 13 SEER outdoor unit, on an old 8 SEER or less indoor coil.
    Feb 2007
    out in the country
    yep, it sounds like a mismatched system
    I never let schooling interfere with my education... Mark Twain
    Exactly, the indoor coil is decade old, but the outdoor unit is quite new. Didn't know that would cause this charging issue.
    Lancaster PA
    Yep, it makes trouble.
    Columbus Ohio
    Please please please say it isn't R-410.
    Lancaster PA
    Is it ok to say its R410A
    South Carolina
    Quote Originally Posted by ggaaxx View Post
    time to call " Joe the HVAC guy" Obama would approve