heat pump Indoor fuse keeps closing
My heat pump worked well during the winter, but when the outside temperature started to climb up around 40F, I had to reset the fuse on my electrical pannel twice already.
The blower kept working even though the heat pump was no longer getting any juice. I only noticed it because the indoor temp started to go down. The Aux heat was set not to kick in above 23F.
The fuse is rated at 30Amps, way above what the heat pump needs at this temp which is around 15Amps according to the manual.
MODEL: ASZ180481A* / CA*F4860*6A*+TXV/ MBE2000**-1 HEATING OPERATION
Outdoor Ambient Temperature
..temp 47 45 40 35 30 25 20
...MBh 62.2 58.9 55.4 51.8 49.5 48.0 44.6
DeltaT 32.9 31.2 29.3 27.4 26.2 25.4 23.6
....KW 3.80 3.72 3.64 3.56 3.52 3.49 3.41
..AMPS 17.0 15.7 14.7 13.8 13.2 13.0 12.2
...COP 4.80 4.64 4.46 4.26 4.12 4.03 3.82
...EER 16.4 15.8 15.2 14.5 14.1 13.8 13.1
.HI PR 398 382 367 351 343 336 323
.LO PR 37 127 119 109 103 99 91
I am planing to call the contractor on monday but any suggestions would be apreciated. Any idea what could cause the indoor fuse to blow like this ?
-
03-14-2009, 08:58 PM #2
Have your contractor check the MCA listing and also the Maximum Fuse Size listing on the model number plate. A 4 ton unit on a 30 amp breaker sounds wrong to me. The wire size also should be checked.
"You do not merely want to be considered just the best of the best. You want to be considered the only ones who do what you do.".... Jerry Garcia
"You just have to decide if you're a Tigger or an Eeyore,..I think you know where I stand on the great Tigger/Eeyore debate." Prof. Randy Pausch
-
03-14-2009, 09:24 PM #3
Regular Guest
- Join Date
- May 2008
- Posts
- 84
-
03-14-2009, 09:26 PM #4
Regular Guest
- Join Date
- Apr 2008
- Location
- St Augustine
- Posts
- 43
That amana max fuse is 40 amp for 4 ton condenser..we have had alot of problems w the amana systems. most of them come over charged from the factory.and head pressures have beed getting up to around 600lbs....
-