    TROUBLE SHOOTING T-X-V

    What are some ways to tell when the super heat is 8 degrees then 0 on a low temp r-404. Tried to open valve couldn't get it right tried to close valve couldn't get it right. Removed sensing bulb noticed that one of the brass screws had made a hole in it could not get power head off so changed valve problem solved. Thought that there was moisture in system all looked good new filter also

  2. #2
    Join Date
    Apr 2008
    Location
    la puente,ca
    Posts
    29
    thats good you fixed it kudos. why do you think there was moisture in the system?

  3. #3
    Join Date
    Nov 2008
    Location
    Hudson Valley, NY
    Posts
    179
    Why do you think that there is moisture in the system?

    Because while the compressor was running, the suction line was frosting up quite heavily and then thawing out quite quickly while compressor was still running and suction pressure was higher than it should have been. That was why I thought there was moisture freezing the valve open.

  4. #4
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,921

  5. #5
    Join Date
    Mar 2008
    Location
    Banana Republic,Florida
    Posts
    400
    Quote Originally Posted by A1 Burt View Post
    What are some ways to tell when the super heat is 8 degrees then 0 on a low temp r-404. Tried to open valve couldn't get it right tried to close valve couldn't get it right. Removed sensing bulb noticed that one of the brass screws had made a hole in it could not get power head off so changed valve problem solved. Thought that there was moisture in system all looked good new filter also
    if you had moisture that valve wouldnt feed your head psi would be everywhere
    by changing out the cores thats a good start i try to change the cores in my stores twice a year cause you alway have that one guy that opens a system and never pulls a vacuum
    Mastic its whats for dinner!

  6. #6
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    52
    Had a call last night at a Pizza supply wholesaler, with 1 - 5 door section out of a 20 door lineup not feeding. pumped system down and found white crystals in TXV strainers( yes water) also found samething in power element . Had to change drier, clean valve, new power element,change drier, vacuum system and charge back up . Also had to heat valve to get ice threw valve. Gotta love it when you get a leak and someone sets LP control in a vaccum for cut out.

  7. #7
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,434
    Quote Originally Posted by A1 Burt View Post
    What are some ways to tell when the super heat is 8 degrees then 0 on a low temp r-404. Tried to open valve couldn't get it right tried to close valve couldn't get it right. Removed sensing bulb noticed that one of the brass screws had made a hole in it could not get power head off so changed valve problem solved. Thought that there was moisture in system all looked good new filter also
    This is a good read.http://hvac-talk.com/vbb/showthread.php?t=162325
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  8. #8
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,921
    Re-read the OP. Did you lose the power element charge? If so, then you have a different problem somewhere else. That will cause a valve to shut down.

    If it is a gas defrost type system, watch your check valves.

  9. #9
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,434
    Quote Originally Posted by jpsmith1cm View Post
    Re-read the OP. Did you lose the power element charge? If so, then you have a different problem somewhere else. That will cause a valve to shut down.

    If it is a gas defrost type system, watch your check valves.
    Opps wrong thread.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  10. #10
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,434
    Quote Originally Posted by crackertech View Post
    Opps wrong thread.
    I take that back he did ask for some trouble shooting tips.

    A1 Burt A1 Burt is offline
    Professional Member

    Join Date: Nov 2008
    Location: Hudson Valley, NY
    Posts: 75
    TROUBLE SHOOTING T-X-V
    What are some ways to tell when the super heat is 8 degrees then 0 on a low temp r-404. Tried to open valve couldn't get it right tried to close valve couldn't get it right. Removed sensing bulb noticed that one of the brass screws had made a hole in it could not get power head off so changed valve problem solved. Thought that there was moisture in system all looked good new filter also
    Reply With Quote
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  11. #11
    Join Date
    Nov 2008
    Location
    Hudson Valley, NY
    Posts
    179
    CRACKER TECH that was a very good read lot's of good imformation thank's

  12. #12
    Join Date
    Feb 2004
    Location
    Medford Oregon
    Posts
    807
    good info on Trouble Shooting TXV's
    http://sporlan.jandrewschoen.com/10-143.htm