    INET sublan comm

    I'm not sure what everyone else's experience is but at our site trying to open the parameters dialogue for a subLan controller takes forever (~30mins). Has anyone figured out a reason for this excessive communication time. Possible fixes?

  2. #2
    Join Date
    Aug 2008
    Posts
    526
    check your ground. only one ground on the whole loop. should not be grounded at every controller. only one point.