    Pros, do y'all close a supply or two in your own home?

    WE have a new HP installed and its blowing a *****in' gale into the mudroom.
    I shut the vent down into that particular room.

    I'll open it if its gonna harm the overall performance

  2. #2
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,288
    Mudroom...how large?

    Personally I leave all supplies open in my own home. None receive too much air. Better solution for your mudroom is for a balancing damper to be installed on the duct that feeds that supply vent. Damper should be installed near trunk line or plenum feeding mudroom supply vent ducting, not right at the supply vent connection.

    Often, when the dampers are throttled closed on a supply vent that feeds too much air, the vent will whistle or give off annoying white noise, which is undesirable. Better to control the amount of air going to that vent at a better location.
    • Electricity makes refrigeration happen.
    • Refrigeration makes the HVAC psychrometric process happen.
    • HVAC pyschrometrics is what makes indoor human comfort happen...IF the ducts AND the building envelope cooperate.


    A building is NOT beautiful unless it is also comfortable.

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    67,721
    Mudrooms should only get enough air to temper them. If they have a door that can isolate them from the rest of the house, and no return in them.

    Although all my registers are open.
    The closing of one register is ok, on any system that has adequate air flow for the system.

    But, its usually better to just balance the system, or throttle down a register in a room you don't need conditioned to normal temp.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Nov 2004
    Location
    Florida
    Posts
    54
    Outside walls have better insulation then inside walls. So you would acutally have more heat loss (or gain) if a inside room was the same temp as outside. You can adjust the supply vent so you don't get to much air but i would not shut it off.

    All vents open.

  5. #5
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    I found that standard residential supply registers are difficult to use for balancing. You'll have much better results paying an installer to add dampers to each supply branch. It's likely the mudroom is located on a section of the main supply trunk that has more restriction, it's located on the very end of the system and gets pressure from the air velocity, it's supply branch is very short or a combination of the above.

    If your supply branches are accessible, it's worth the money to have dampers installed on most if not all the branches and balance the system. The goal is that the airflow to each room is proportional to it's heat loss or gain so no matter how long or how often the system runs, all rooms stay roughly the same temperature.

    It made a huge difference in my home and eliminated noise from the registers.

    Adjusting airflow using the registers just makes a system noisy.

  6. #6

    Actually no

    Quote Originally Posted by motoguy128 View Post
    I found that standard residential supply registers are difficult to use for balancing. You'll have much better results paying an installer to add dampers to each supply branch. It's likely the mudroom is located on a section of the main supply trunk that has more restriction, it's located on the very end of the system and gets pressure from the air velocity, it's supply branch is very short or a combination of the above.

    If your supply branches are accessible, it's worth the money to have dampers installed on most if not all the branches and balance the system. The goal is that the airflow to each room is proportional to it's heat loss or gain so no matter how long or how often the system runs, all rooms stay roughly the same temperature.

    It made a huge difference in my home and eliminated noise from the registers.

    Adjusting airflow using the registers just makes a system noisy.
    the AH is in the attic right on top of the mudroom (8x8) and is blowing a zephyr into the room.

  7. #7
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    Quote Originally Posted by AvantGarde View Post
    the AH is in the attic right on top of the mudroom (8x8) and is blowing a zephyr into the room.
    Yup...that pretty much sums up the problem. The supply may even be located on the supply plenum, which is generally considered a bad idea because it's noisy, and can be very hard to balance even with a supply damper.

    Sounded like DIY instructions

    I had a similar problem with by 2 back bedrooms that were located near the furnace in the basement. Their supplys were attached to the supply plenum 6" above the indoor coil. Even with the dampers mostly clsoed they were still noisy and had too much airflow while the front of the house was starved for air. The solution was to add a new 8"x10" branch to feed both supplies. This eliminated to noise but actually went a little too far the opposite way since hte total lenght of the ductwork was increased. I think now a 8"x12" would have been about perfect.
    Last edited by beenthere; 03-10-2009 at 11:17 AM. Reason: Removed DIY instruction paragraph

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event