    York XL Trouble Output to York IAQ Thermostat

    Is there any method to connect a York Heat Pump's X/L output (trouble status) to a Honeywell Vision Pro IAQ thermostat so that the user can see the trouble flashes? My 20 year old Lennox thermostat could do this, but the York service folks say the IAQ has no capability in this regard.

    RJ
    Quality Remains Long After the Price is Forgotten

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    70,437
    Post Likes
    The IAQ has a terminal for it.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Jul 2003
    Location
    Texas Hill Country
    Posts
    254
    Post Likes
    Thanks,that was it. The EIM install manual had nothing in it about L even though it is labeled on the board. The installer got it working with your info