    Thumbs down It was working


    Duct was not connected to electronic filter cabinet. Like the new style electronic filter?



    Insulation pulled out of the cabinet. Look at the mold!



    Picture snapped right before the internal relief went off in the scroll.

    System specifications:
    3 year old Carrier
    38YCC048 matched to FA4ANF060
    7/8" x 5/16" line set [50']
    400+ psig after stone cold start and 2 minutes of operation.[heat mode]
    [6] 6 x 14 return grills pulled through wall cavities
    Maximum test static .67" wc. Actual static .78" wc. and pulsating
    Aluminum wire [no disconnect]
    15 kW strip heater [only 10 kW connected]
    Condenser "pigtail" not connected [insulation of wiring rubbing cabinet]
    Duct not sealed
    The list goes on

    Where does this stop? This was done by one of the largest contractors in the area. Bigger is better, Right!?

    [Edited by Boss on 12-28-2003 at 09:59 PM]

  2. #2
    Join Date
    Aug 2002
    Location
    Office and warehouse in both Crystal River & New Port Richey ,FL
    Posts
    18,836
    Need a better picture,but a great installation to point HO's to when they want to know which brand is best/most dependable.

    Was this new constuction or a changeout?I'd send the photo and the HO to Carrier Corp. from some help,or fix it and send them to their lawyer!!

  3. #3
    Join Date
    Nov 2002
    Location
    Piedmont Triad area of North Carolina
    Posts
    2,300
    Dash,

    This was a change out...and a pitiful one at that!! I used to work for this company and this really disturbed me. Pardon my French, but their quality went to Sh1t! They use to do some of the best work around, but greed took over!

  4. #4
    Join Date
    Oct 2001
    Location
    Clyde, Ohio
    Posts
    114
    400 PSIG in 2 min. I sugest you run
    If you do it yourself, You only have yourself to blame

  5. #5
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Ya mean 410a isn't a drop in right over top of a leaking 22 system?????

  6. #6
    Join Date
    Nov 2002
    Location
    Piedmont Triad area of North Carolina
    Posts
    2,300

    Talking

    R-422...have not heard of that one Dave...LOL

  7. #7
    Join Date
    Jul 2002
    Location
    Zelienople, Pa
    Posts
    2,965
    This was a change out...and a pitiful one at that!! I used to work for this company and this really disturbed me. Pardon my French, but their quality went to Sh1t! They use to do some of the best work around, but greed took over!


    ARS???

  8. #8
    Join Date
    Nov 2002
    Location
    Piedmont Triad area of North Carolina
    Posts
    2,300

    Talking

    GOOD GUESS...But wrong!

    Just about as bad!!

  9. #9
    Join Date
    Sep 2001
    Location
    East Stroudsburg, PA
    Posts
    13,215
    Originally posted by dakers
    R-422...have not heard of that one Dave...LOL
    Gee, maybe we could talk someone we don't like into trying that...


    Wonder what the unit would look like after it stopped?