    Confused Commisioning DX9100

    Hopefully you Jci Guys can help me out.
    Today I uploaded the controller info (DX9100) using GX9100.
    I then tagged all the AI,AO,DI's,DO's
    I then renamed the .DXS file to a .DMO file
    I then converted the .DMO to a DLL
    Thats as far I got>
    [I] could not open the DLL file with DX9100 commisioning tool or HVACPRO
    When I tried I got an error stating the template did not match the device.
    I could use some professional guidence
    Thank you
    If you cant fix it right, try again.

  2. #2
    Join Date
    Sep 2008
    Posts
    51
    Use the DMO file with DX9100 commissioning tool. Hvacpro is not for DX9100.

  3. #3
    Join Date
    Jun 2001
    Location
    Northwest Indiana
    Posts
    1,312
    Quote Originally Posted by dx9100 View Post
    Use the DMO file with DX9100 commissioning tool. Hvacpro is not for DX9100.
    I was desperate and was willing to try anything(amAture I know)
    It seems when opening the the dll via dx comissioning tool that the DLL is corrupt.
    What I mean to say is once you select the file, normally the points appear in the window.
    That does not happen.
    I know Im effing something, just not sure.
    I'm reading the help files for the gx and the dx commisioning tool right now.
    I also down loaded the users guides off johnson's website.
    Alot to read by tomorrow.
    The Goal is to see whats going on real time
    If you cant fix it right, try again.

  4. #4
    Join Date
    Feb 2008
    Posts
    225
    Actually you can commission a DX-9100 with HVACPRO.

    After you created a DMO file.
    Open the DMO file in Wordpad.
    Get rid of all the points/modules that you won't be using and save it.
    Open HVACPRO and at the bottom, there is a drop down arrow.
    Change CFG to DMO.
    Then go to open and select your dmo file.
    Then go and select action , commission current config.
    It should work.

    By the way what GX version do you have and
    what HVACPRO version do you have?

  5. #5
    Join Date
    Jun 2001
    Location
    Northwest Indiana
    Posts
    1,312
    Gx version is 7.05
    DX commisioning tool is v8.08
    hvac pro is 8.08b
    If you cant fix it right, try again.

  6. #6
    Join Date
    Jun 2001
    Location
    Northwest Indiana
    Posts
    1,312
    I did not create a dmo, i uploaded a dxs file via gx 9100 and renamed it to a dmo file.
    If you cant fix it right, try again.

  7. #7

    Try this

    open the .DXS file w/ GX9100
    on Flle meno, select DDL File Options
    place check in - Generate DDL On File Save
    click ok
    click save
    this should create your .DMO file which is then opened w/ Commisioning tool

  8. #8
    Join Date
    Apr 2008
    Location
    chicago
    Posts
    115

    Do Not Rename the .dxs file

    Use the file option to generate the ddl on file save. This will create your .dmo file. (It also creates a .dnc file, but you use the .dmo file for commissioning.) If your .dmo file contains too many points for the commissioning program it will lop off the points at the end. I usually then edit the .dmo file with a text editor to delete unnecessary points. I rename the file ending with a "c" so I know that is my commissioning file.

  9. #9
    Join Date
    Aug 2002
    Location
    Rochester,MN
    Posts
    131

    re:DX-9100 download

    I have my laptop connected to our DX and I want to download a XT module to re-boot it with a backup copy I downloaded from my PC. What is the simpleless steps to use? Thanks!

  10. #10
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    1,458
    Quote Originally Posted by tegger View Post
    I have my laptop connected to our DX and I want to download a XT module to re-boot it with a backup copy I downloaded from my PC. What is the simpleless steps to use? Thanks!
    tegger, start a new thread please. This could get confusing, O.K.
    If sense were so common everyone would have it !

    All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!

  11. #11
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    1,458
    Toptech,
    I copy the *.dmo (after following the ddl on save instructions on PP) file then rename IT (the copy of the *.dmo) to *.ddl. Once done edit the *.ddl file and use it in DX-Commissioning. That way if you find you are missing a necessary point in the DX template (*.ddl file) you can open notepad twice and copy from the *.dmo to the *.ddl file and still have the *.dmo unchanged.

    For future reference the *.dxs file is ONLY useable in GX-9100 so just leave it alone (don't rename it).

    Also, if you can teach yourself DX-9100 from that manual you are a better man than I ! I honestly believe that is JCI's worst manual.....ever !

    Good Luck, you're gonna need it !!!!!!
    If sense were so common everyone would have it !

    All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!

  12. #12
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    1,458
    Look in the "Junk Yard" (advertisment) a DX Demo Case might help you !


    (Am I gonna get in trouble for this ?)
    If sense were so common everyone would have it !

    All opinions expressed are my own. Any advice provided is based on personal experience, generally accepted fact or publicly available information. As such, it is worth exactly what you paid for it, not a penny more not a penny less !!

  13. #13
    Join Date
    Jun 2001
    Location
    Northwest Indiana
    Posts
    1,312
    Quote Originally Posted by CCIKelly View Post
    Look in the "Junk Yard" (advertisment) a DX Demo Case might help you !



    (Am I gonna get in trouble for this ?)
    Thanks I will
    If you cant fix it right, try again.

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event