Results 14 to 15 of 15
    Mar 2009
    Luxaire w/ 2 zones
    I've been out of residential for a long while. I'm currently planning a job for a 2 story house in northern NJ. 700sq ft on both the 1st and 2nd floors. The home owner ripped out the boiler and all of the piping throughout the house because he was determined to have a furnace put in.
    I'm planning on using a Luxaire AL8B048F1 condensing unit w/ a LP9C120D20MP11 mod furnace. The system will be zoned w/ 2 zones of equal size.
    1. Is this condensing unit a 2spd?
    2. What is the btu capacity of the compressor in low spd? Is it half of the total capacity?
    3. What damper system do you recommend?
    4. Does Coleman make an equivelant system?
    I decided on the mod furnace so I didn't have to run a bypass damper. Im not a fan of recirculating conditioned air back into the furnace w/ the possibility of it going off on limit or freezing the coil.
    Any feed back would be appreciated
    Ray
    Quote Originally Posted by heeltoe View Post
    Do a load calc. 4 tons of cooling, and 120,000 BTUs of heat for 1400 sq ft???? Must have 40 foot high ceilings.
    Yes.
    Compressor capacity is 67% in first stage, system capacity is 70%+ in first stage.
    Honeywell, with the Honeywell Evirozone panel
    Yep
    Still going to need a bypass damper.
    Ray
    Get a contractor to do this job for you.