Thread: typical hi RH-winter, here

  1. #1
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes

    typical hi RH-winter, here

    at 6am, dry bulb= 23F, wet= 21F = ~95%RH
    so,
    sealing attics & crawlspaces prevents sucking in moist air;
    probably best to forget vapor barrier --

    this hi RH will typically be until 10am --

    so,
    don't make firm statements that one should draw in outside air;
    unless
    it is conditioned --
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

  2. #2
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    It's 95% RH... the key term is RH. That amount of moisture at the indoor temp of 70F, is only around 25%RH if I read my Psychrometric chart right.

    A <25F dewpoint is still pretty dry.

    Maybe I'm understanding your statement wrong. As a pro, I'd think you'd know this already. The saturation point of air it terms of how much moisture it will hold decreases as temeprature decreases. So saturated air at 20F, hold 1/4 the amount of moisture as air at 70F.

    Ideal conditions of 40-45% RH at 70F is a dewpoint of around 45-50F. So to better understand this, if the home is an idea 45% RH at 70F, then any indoor surface that is <50F will have moisture on it. This is why windows have moisture at low outdoor tempratures.

  3. #3
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I could be wrong.

    But, at 23°F DB and 21°F WB the RH is 75.1%, 13.0588 grains per pound of air.

    At 70°F DB and the same 13.0588 grains of moisture, it would be 12%RH.

    According to my Carrier chart.

  4. #4
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by beenthere View Post
    I could be wrong.

    But, at 23°F DB and 21°F WB the RH is 75.1%, 13.0588 grains per pound of air.

    At 70°F DB and the same 13.0588 grains of moisture, it would be 12%RH.

    According to my Carrier chart.
    You are correct on both counts.

    cems-bee wrote:
    so,
    sealing attics & crawlspaces prevents sucking in moist air;
    probably best to forget vapor barrier --
    this hi RH will typically be until 10am --
    so,
    don't make firm statements that one should draw in outside air;
    unless
    it is conditioned --
    Beenthere (along with motoguy) is correct again, in that drawing in air under the conditions you gave is still dry air, and will lower indoor RH levels if not humidified (or if indoor moisture generation is low).

    Any vapor barrier, to my understanding, should be on the drainage plane of a wall (behind the siding or cladding, in front of the sheathing), not on the interior. Housewraps are air and liquid moisture barriers, but allow vapor diffusion (allowing a wall cavity to dry to the exterior as well as to the interior).
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  5. #5
    Join Date
    Feb 2007
    Posts
    1,002
    Post Likes
    Quote Originally Posted by shophound View Post
    You are correct on both counts.

    Any vapor barrier, to my understanding, should be on the drainage plane of a wall (behind the siding or cladding, in front of the sheathing), not on the interior. Housewraps are air and liquid moisture barriers, but allow vapor diffusion (allowing a wall cavity to dry to the exterior as well as to the interior).
    How about fiberglass insulation w/paper vapor barrier, applied to the sill (not sure if this is the correct term, but is first wood above grade on top of cinder block).

    The barrier is on the inside face of the insulation.

    Thanks.

    Amp

  6. #6
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by ampulman View Post
    How about fiberglass insulation w/paper vapor barrier, applied to the sill (not sure if this is the correct term, but is first wood above grade on top of cinder block).

    The barrier is on the inside face of the insulation.

    Thanks.

    Amp
    Do you mean something like this, where a framed stem wall sits on top of the basement wall or crawl space wall? :



    In the drawing, notice the lack of a vapor barrier to the interior, and why. The interior plane shows drywall painted with latex, to allow drying of the wall cavity via vapor diffusion to the interior.

    If you're speaking about a different configuration (such as an above grade block house) please specify where this is found in the house.
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  7. #7
    Join Date
    Feb 2007
    Posts
    1,002
    Post Likes
    Quote Originally Posted by shophound View Post
    Do you mean something like this, where a framed stem wall sits on top of the basement wall or crawl space wall? :

    Yes, this is a basement w/10 ft cinder block walls. The cinder block extends about 1.5 feet above grade. There is an attached crawl space which has the same treatment.

    In the drawing, notice the lack of a vapor barrier to the interior, and why. The interior plane shows drywall painted with latex, to allow drying of the wall cavity via vapor diffusion to the interior.
    The basement is unfinished; hence no interior walls.

    Would I assume correctly, that my 'configuration' doesn't pose any problem?

    Thanks.

    Amp

  8. #8
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,847
    Post Likes
    Quote Originally Posted by ampulman View Post
    Yes, this is a basement w/10 ft cinder block walls. The cinder block extends about 1.5 feet above grade. There is an attached crawl space which has the same treatment.



    The basement is unfinished; hence no interior walls.

    Would I assume correctly, that my 'configuration' doesn't pose any problem?

    Thanks.

    Amp
    The fiberglass batts...are they attached to the basement wall, or the crawl space wall? Is the basement wall exposed block, or does it have a framed wall in front of the block to contain insulation? The crawl space...is it ventilated? Is the floor over the crawl space insulated?
    Psychrometrics: the very foundation of HVAC. A comfort troubleshooter's best friend.

  9. #9
    Join Date
    Jan 2009
    Location
    SE Iowa
    Posts
    5,577
    Post Likes
    Quote Originally Posted by beenthere View Post
    I could be wrong.

    But, at 23°F DB and 21°F WB the RH is 75.1%, 13.0588 grains per pound of air.

    At 70°F DB and the same 13.0588 grains of moisture, it would be 12%RH.

    According to my Carrier chart.
    That's probably right. I just "eyeballed" a chart I found on google that wasn't specific to HVAC. The Carrier chart is probably a little more precise (easier to read). I had to convert from celcius as well.

  10. #10
    Join Date
    Feb 2007
    Posts
    1,002
    Post Likes
    Quote Originally Posted by shophound View Post
    The fiberglass batts...are they attached to the basement wall, or the crawl space wall? Is the basement wall exposed block, or does it have a framed wall in front of the block to contain insulation? The crawl space...is it ventilated? Is the floor over the crawl space insulated?
    The basement wall (cinder block) is below grade, with the exception of about 1.5 ft. On the top block (above grade), there is an approximately 2 x 5" board laid flat, on which 2 x 8 joists are placed. At the top of joists is the first level sub-floor. This (8") is the space which contains the (kraft paper inward) faced fiberglass. This is all open to the basement.

    The crawl space is basically the same, except that the joist level is split (lowered) from the main (first floor) about 8". The crawl space is under a section of house which has no second floor, and contains heating ducts, pvc furnace vent pipes, and plumbing.

    There is fiberglass (about 1") board on the walls; some thick material on the floor. The space is open to the basement and is not vented to the outside. It is on the cool side.

    Thanks.

    Amp

  11. #11
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes
    Thread Starter
    read about vapor barriers at BUILDINGSCIENCE.com

    so, I did not carefully note my dry bulb, I focused on the wet bulb & RH%.

    nevertheless, every thing I have heard or read from the health 'experts' is that RH% should be kept between 35 & 55%.
    No body stated that it was dependent upon temperature.
    so, maybe my bdrm @ 57F does not have much moisture per cubic ft, but it is still on the high side [60+ percent], especially during the early morning --
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    If you know WB and RH, you can find/determine DB.

  13. #13
    Join Date
    Feb 2003
    Location
    Huntsville,AL
    Posts
    4,125
    Post Likes
    Thread Starter
    why look-up or calculate when I can just read my instrument?
    I suspect that I did my first look-up in 1961 --

    again, what is your 'take' on RH% needed ID for good health, even at 57F?
    at 67F?
    harvest rainwater,make SHADE,R75/50/30= roof/wall/floor, use HVAC mastic,caulk all wall seams!

  14. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    I said calculate it, because if you only keep records of WB and RH, you can use them to know what it was in those years that you didn‘t track DB..

    I don’t believe there is one set range of RH for everyone.

    If in the heating season, you wake up in the morning, and your throat is dry and scratchy. Your RH is too low for you. And that is unhealthy.

    Same way, if you wake up and your sweating, its to high, or the temp is too high for the RH.

    If you set your humidistat at a setting that both keeps the dust down, and your throat from drying out. Plus your not condensing or frosting up your windows. That’s the RH that is probably best for you, and your home.

  15. #15
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by cem-bsee View Post
    read about vapor barriers at BUILDINGSCIENCE.com

    so, I did not carefully note my dry bulb, I focused on the wet bulb & RH%.

    nevertheless, every thing I have heard or read from the health 'experts' is that RH% should be kept between 35 & 55%.
    No body stated that it was dependent upon temperature.
    so, maybe my bdrm @ 57F does not have much moisture per cubic ft, but it is still on the high side [60+ percent], especially during the early morning --
    Here is what we are all tring to tell you. You need a little some of that 23F, 95%RH air in your to get you bedroom below 50%RH. When home have high %RH during cold weather, they are not getting enough fresh air to remove the moisture generated by the occupants. You need an air change every 4-5 hours to pruge the indoor pollutants. That would make your home dry when the outside dew point is below 32^F, 100%RH.
    Its about the water content of the outside air. A plastic bag of 32^F100%RH, 32^F dew point warmed upto 57^F is 40%RH.
    You are not getting enough fresh air into your home remove the moisture. A couple in a +2000 sqft. home will with an air change every 5-6 hours will be a little on the dry side, <35%RH with a 23^F outdoor dew point. Generally, homes that are getting enough fresh air during cold weather are dry. You know the rest of the story. Homes that are getting enough fresh during wet high dew point weather are wet, unless they have 30-70 lbs. of moistue removed per day (a/c or dehumidifier). During 65^F outdoor dew points, a properly venitlated home needs +30lbs. of dehumidification per day. Regards TB
    Last edited by teddy bear; 03-10-2009 at 01:50 PM. Reason: missing words
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •