  1. #27
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,343
    Post Likes
    I had that K42 relay go bad on me also, swapped with a unit next to it and same problem moved there. Mine had a Tr 100 drive in it though.
    UA Local 32

  2. #28
    Join Date
    Jan 2013
    Location
    South of GA
    Posts
    121
    Post Likes
    Thread Starter
    Quote Originally Posted by buford View Post
    I had that K42 relay go bad on me also, swapped with a unit next to it and same problem moved there. Mine had a Tr 100 drive in it though.
    Buford, thank you for taking the time to respond, have you been reading all the comments??, are the symptos we are having similar to the ones you were having when you had the same problem?????

  3. #29
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    19,034
    Post Likes
    Yo, Wild Cat . . .

    Tried sending you a Trane VFD tech phone number to the email address in your profile, but it got bounced back. If you want to update that profile, I'll try again. Otherwise, sometimes there will be an 800 number right on the drive.
    A skilled Tech would solder a relay on that board and call it good to go.

  4. #30
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,343
    Post Likes
    very similar, as Jay said you need to verify on the drive, the enable contact to verify it is closed or calling for the drive to run, If i remember that relay closed 2 wire to the drive to run. Find K42 relay on the small inset wiring diagram that is on the main diagram and see how this relay works. I put a bypass jumper on it and my drive started up. As said the old relay just would not make its contacts at times.It was a pain cause you would reset power and the next 10 tries it would work fine. I waited till the next call and went right to the relay and jumped it out.
    UA Local 32

  5. Likes BBeerme, GoCougs liked this post
  6. #31
    Join Date
    Jan 2013
    Location
    South of GA
    Posts
    121
    Post Likes
    Thread Starter
    Quote Originally Posted by BBeerme View Post
    Yo, Wild Cat . . .

    Tried sending you a Trane VFD tech phone number to the email address in your profile, but it got bounced back. If you want to update that profile, I'll try again. Otherwise, sometimes there will be an 800 number right on the drive.
    BBeerme, strange !! Just got an email from one of the guys here, last night I will check it out., thank you.

  7. #32
    Join Date
    Jan 2013
    Location
    South of GA
    Posts
    121
    Post Likes
    Thread Starter
    Quote Originally Posted by buford View Post
    very similar, as Jay said you need to verify on the drive, the enable contact to verify it is closed or calling for the drive to run, If i remember that relay closed 2 wire to the drive to run. Find K42 relay on the small inset wiring diagram that is on the main diagram and see how this relay works. I put a bypass jumper on it and my drive started up. As said the old relay just would not make its contacts at times.It was a pain cause you would reset power and the next 10 tries it would work fine. I waited till the next call and went right to the relay and jumped it out.
    Buford, thank you taking the time to respond, will look for that relay tomorrow, that relay must be 24 volt , correct?????' Thank you.

  8. #33
    Join Date
    Sep 2007
    Location
    edmonds wa
    Posts
    4,343
    Post Likes
    I am not sure , either pull the relay and look on the diagram. 120v first thing that i remember.
    UA Local 32

  9. #34
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    4,623
    Post Likes
    Just cause you hear click, doesn’t mean diddly.....USE YOUR TOOLS!!

    A drive needs three things to run, 4 if you include power.:

    1: a start enable command (usually a dry contact relay.

    2: all safety and interlock circuits closed.

    3: a Control signal to tell what speed to run at.

    Lacking any one of these three and the drive will not run. You verified the control signal, still have 2 to go.

  10. Likes manny238 liked this post
  11. #35
    Join Date
    Jan 2013
    Location
    South of GA
    Posts
    121
    Post Likes
    Thread Starter
    Quote Originally Posted by 71CHOPS View Post
    Just cause you hear click, doesn’t mean diddly.....USE YOUR TOOLS!!

    A drive needs three things to run, 4 if you include power.:

    1: a start enable command (usually a dry contact relay.

    2: all safety and interlock circuits closed.

    3: a Control signal to tell what speed to run at.

    Lacking any one of these three and the drive will not run. You verified the control signal, still have 2 to go.
    71CHOPS, haha a click won’t tell us anything right??, this morning I’m back at the job and check the K42 relay and it is closing the NO contacts and sending power to the Drive, I had to call the manufacturer square D tech support and after some troubleshooting they diagnosed that the drive is severely damage we are ordering a new one, I want to thank everyone of you that pitched in your 2 cents of wisdom on this issue, God bless you all. I will pist when we replaced it,

  12. #36
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    4,623
    Post Likes
    Cool, thanks for the update!

  13. #37
    Join Date
    Apr 2006
    Location
    s.c.
    Posts
    1,816
    Post Likes
    ah, the ol square d to tr200 conversation

  14. #38
    Join Date
    Apr 2008
    Location
    Tucson, AZ
    Posts
    277
    Post Likes
    I would not like to thank some manufactures for sticking the VFD inside next to the blower so you can stick your head in there while it's running.

  15. #39
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    29,299
    Post Likes
    One of the small things that Lennox has done right is to put the MSAV controller in the control section.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  16. Likes mccann liked this post