Results 1 to 4 of 4
Thread: Humidifier Rec
    Nov 2017
    Humidifier Rec
    Hoping someone can give me a rec for a steam humidifier. This unit would have to serve approximately 6000 sq ft (4 zones, 3 floors + finished basement) 9ft ceilings. Only one handler is in the basement, so that is the one that will get the humidifier).
    Seems like would need to handle a load of 13 lbs/hr, about 40 gallons per day. Suggestions?
    (As a side, I would have liked to have installed more units, but have been warned against installing anywhere other than a basement...)
    Jun 2014
    Dover, DE
    If you have the electric available, and airflow, I like these.
    http://www.carelusa.com/immersed-ele...0D2E4B60ED7A22
    These can also be remotely mounted and steam line piped to the ductwork. Within a reasonable distance.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison
    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi
    "In this house we obey the laws of thermodynamics" - Homer Simpson
    Madison, WI/Cape Coral, FL
    Quote Originally Posted by ApplesNYC View Post
    13 lbs. per hour with steam/electric cost minimum of 5 kwh per hour plus a lot of cleaning the sludge in the pot every 2-4 weeks. This could be $+12 per day.
    Suggest a couple of large by pass humidifiers with a a 200-300 cfm duct and use the heat from the heat pump/gas heater which would 50-75% less cost.
    This will take once a year new pads.
    The large Aprilare by pass is rated at 5-6 lbs. per hour. Locate in basement with next to the heating system. This assumes that the fan on the heating system operates 24/7 on low speed. To get high air flow through the humidifier, a second duct fan will be needed. You will 2-3 large by-pass humidifiers. A second duct fan is needed to get the 200-300 cfm air flow per humidifier to max the evaporation capacity of the humidifier.
    If you are not ready for an adventure, do not try this.
    I have done with success. The key is the high air flow through the humidifier. It will save your customer a ton of money using the space heat source verses the electricity to evaporate the moisture.
    You could just put 3 by pass humidifiers on your heating system and operate the fan on high speed and get some humidification. May work well.
    Keep us posted.
    Regards Teddy Bear
    Nov 2017
    Thanks for recs and thanks TB.
    Quick follow up - and sorry if this is a dumb question - but I read this as putting 2-3 bypass humidifiers together? This does sound like an adventure!