    York RTU odor and found wet insulation

    Company installed a 5 and a 4 ton York . Been in since June. I was asked to check odor. Not a burn smell, not incomplete combustion smell, I recognized the odor. I pulled side discharge cover and found one unit had insulation touching heat exchanger-corrected. Checked gas pressure 3.5-3.5 ok. Then noticed drip. Both units interior insulation above heat exchanger wet. That was odor! Wet insulation. No water on top of units. We have had many units like this ,no water. Asked tech support if any reported issues,told to investigate. I am going back to check combustion. Perform air flow calculation per York dry coil pressure differential. Need to take temp diff on heat xch. Just ran out of time today. Any ideas?

  2. #2
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    4,601
    Post Likes
    Condensation from air infiltration?

  3. #3
    Join Date
    Sep 2010
    Posts
    95
    Post Likes
    Thread Starter
    OA dampers closed, serves office area

  4. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    29,233
    Post Likes
    Airflow too high, pulling water off the evap?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  5. #5
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    14,599
    Post Likes
    Quote Originally Posted by OhioTech View Post
    OA dampers closed, serves office area

    Too much hot air/gossip/BS in the office?
    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"

    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."

    Jtrammel - "I’m going to sell hvac systems derp derp derp"
    BBeerme - "every time he opens his mouth, he reminds me of a cow without the fart bag."

  6. #6
    Join Date
    Dec 2003
    Location
    Northern VA
    Posts
    685
    Post Likes
    How are your return air grilles. Are they clean.