    Digicool Temperature Accuracy
    My digicool clamps are about 10 degrees off from my Fluke 52II WITH 80pk clamp. What’s the most accurate way to see which one is wrong?
    Dec 2014
    Edmonton, Alberta, Canada
    Put both probes in a glass of water with ice and see which hit 32F.
  3. Likes mark_kershner, N2fords liked this post
  4. #3
    Nov 2007
    Tucson, AZ
    might want to be sure both batteries are new or good at least.
  5. #4
    Dec 2014
    So which sensor was wrong? My money is on the Fluke K-type.
  6. #5
    Quote Originally Posted by Apocapants View Post
    Haven’t checked yet. Been too busy. I’m just banking on the digicool being correct for now. They are closer on air conditioning temp range. The huge discrepancy was when checking superheat on freezer with suction line temp below 0
  7. #6
    Oct 2010
    digicool uses 10k thermistors so they are more accurate. I’ve never had a thermistor read “off”, they either read correctly for their Ohm/temp curve or they read open.
    K type thermocouples are notorious for being “off” by several degrees. Even a $175 fluke one.