    They mixed up the valves on me

    I thought the red was for Name:  1507829844973-1818234396.jpg
Views: 254
Size:  68.1 KBhigh pressure or liquid and blue was for low pressure or vapor.
    A skilled Tech would solder a relay on that board and call it good to go.

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,150
    Post Likes
    you got yourself a propane tank valve setup there.
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  3. Likes Nuclrchiller liked this post
  4. #3
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    6,150
    Post Likes
    double post
    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Political Correctness is forced on you because you have forgotten decency.

  5. #4
    Join Date
    Jul 2014
    Location
    Sarasota, Florida
    Posts
    244
    Post Likes
    I've had that happen aswell

  6. #5
    Join Date
    Nov 2008
    Location
    Long Island NY
    Posts
    759
    Post Likes
    Happened to me a few times also.

    Sent from my SM-N910T using Tapatalk

  7. #6
    Join Date
    Dec 2014
    Location
    midwest
    Posts
    1,873
    Post Likes
    Quote Originally Posted by GettnBetter View Post
    I've had that happen aswell
    X2

    Sent from my SM-G930V using Tapatalk

  8. #7
    Join Date
    Dec 2007
    Posts
    8,002
    Post Likes
    Got one like that.
    It threw one of our techs off when he tried to reuse what he pumped into it.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  9. #8
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    4,595
    Post Likes
    One of the guys that helped train me, was an older chiller tech.....he said, "ALWAYS check to make sure the valves actually are correct before charging!!" He had a BAD experience with a chiller because of that.

  10. #9
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    18,904
    Post Likes
    Thread Starter
    Here's what happened today.

    Leak check and repair. Two stage, maybe a 10 ton package unit, tonnage matters little here. Found leak, recovered, repaired, then went to do the leak check. I always use the vapor off of the top of the recovered refer and charge to 15 psig. Then top up with nitro to 150 psig.

    Just that today I saw the high side hose jumping as though it had liquid going through it. Wasn't too concerned. Then it hit me, something was wrong. I shut all the valves as fast as I could. Then just stood there. Trying to figure out what I did wrong.

    Then saw the labeling on the handles. I'm like, crap. Well, at least there is so much R-22 in the system. Don't need no freakin' nitro for leak checking. Kinda sorta pissed me off; is this tank from Mexico, China, or Tennessee??
    A skilled Tech would solder a relay on that board and call it good to go.

  11. #10
    Join Date
    Nov 2011
    Location
    East Side
    Posts
    4,595
    Post Likes
    You'd likely still need higher pressure to show all leaks. You might have put a pound or so into it. I would have thrown nitrogen on top and went with it.

    I may put 5 lbs in a 1,000 ton chiller, plus nitrogen pressure.

    I don't believe there is an actual percentage listed for "trace gas" In the EPA ruling.

  12. #11
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    18,904
    Post Likes
    Thread Starter
    My rule is 10% trace gas. Then nitro up to 150 psig. The H-10G is an awesome piece of equipment.

    With R-22, and 90% R-22, repairing a known leak, 25 psig would probably do it.

    Kind of a sad story, just today, got a call . . . Ooops, open forum . . .


    Quote Originally Posted by 71CHOPS View Post
    You'd likely still need higher pressure to show all leaks. You might have put a pound or so into it. I would have thrown nitrogen on top and went with it.

    I may put 5 lbs in a 1,000 ton chiller, plus nitrogen pressure.

    I don't believe there is an actual percentage listed for "trace gas" In the EPA ruling.
    A skilled Tech would solder a relay on that board and call it good to go.