    Found this friday
    On a MANITOWOC ice machine.
    Our company got called after another contractor.
    Yeah thats a HPR valve put in place of txv.
    LOL

  2. Likes joejax liked this post
  3. #2
    Join Date
    Jun 2017
    Posts
    24
    Post Likes
    Thread Starter
    Name:  IMG_5121.JPG
Views: 180
Size:  98.3 KBName:  IMG_5122.JPG
Views: 176
Size:  77.1 KB

  4. #3
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    2,073
    Post Likes
    Lol.

    Sent from my SM-N910W8 using Tapatalk

  5. #4
    Join Date
    Aug 2013
    Location
    Omaha
    Posts
    2,793
    Post Likes
    LOL

    Sent from my SM-N920V using Tapatalk

  6. #5
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    1,085
    Post Likes
    Uh.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  7. #6
    Join Date
    Feb 2016
    Location
    Florida
    Posts
    387
    Post Likes
    Errr....was it making ice? ;/

  8. #7
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    5,897
    Post Likes
    Clear example of an experienced tech making the diagnosis and sending a greenhorn out to make the repair.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  9. #8
    Join Date
    Jun 2017
    Posts
    24
    Post Likes
    Thread Starter
    It was not producing ice.
    The coustomer said it made a few pieces the day they repaired it.
    When i got there the refrigerant had all leaked out.
    The brazing on suction side has a leak and low side shrader valve core leaks.
    The error log on Indigo controller showed repeatedly High pressure cut out
    Faults.
    I'm not sure what the original problem was ,i am assuming it was low on charge due to shrader valve core leak.
    I'm going back Monday with a new txv .
    BAKER supply had to order.
    Once i get new txv installed and replace shrader cores I will see what i get.
    I will repost what results are.

  10. #9
    Join Date
    Nov 2006
    Location
    Wisconsin
    Posts
    476
    Post Likes
    Lol, nice find. Maybe the parts house screwed up, and the tech they sent was too green to know it was the wrong part.
    The remote condenser machines do use an hpr valve.

  11. #10
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,822
    Post Likes
    No. Way.