    Question Less BTUs Blowing Colder

    I have a older window AC unit thats 8,000 btus and a brand new lg unit thats 15,000 btus. The newer bigger unit is blowing 3-4 degrees warmer(53 F) than the smaller older unit(50 F)... whats going here? both are on the high fan setting.

  2. #2
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    10,190
    Post Likes
    BTUs are only a capacity measurement. Temperature is based upon efficiency, air flow, loadings, and amount of refrigerant.
    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"
    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."

  3. #3
    Join Date
    Aug 2017
    Posts
    3
    Post Likes
    Thread Starter
    ignore

  4. #4
    Join Date
    Aug 2017
    Posts
    3
    Post Likes
    Thread Starter
    Quote Originally Posted by HVAC_Marc View Post
    BTUs are only a capacity measurement. Temperature is based upon efficiency, air flow, loadings, and amount of refrigerant.
    what does my situation mean then

  5. #5
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    10,190
    Post Likes
    It means that you should quit worrying about it. It will work fine. Something as simple as the fan spinning a little faster could cause a higher temperature coming off the coil.

    Even identical units from the same manufacturer are different.
    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"
    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."

  6. #6
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    17,144
    Post Likes
    It's more efficient than the old one. It's working as designed. Case closed.

  7. Likes BaldLoonie liked this post
  8. #7
    Join Date
    Jun 2017
    Location
    Rockledge, Florida.
    Posts
    36
    Post Likes
    The capacity of the unit is a measurement of how much energy is being pulled out of the indoor air and moved outside. The energy exchange is a function of the amount of humidity removed from the air (latent energy) and the change in temperature of the air (sensible energy). Both of those are heavily affected by the mass flow of air moving through the air conditioner. The larger unit almost certainly has a much larger mass flow of air due to having a larger fan. To do a capacity comparison you would need to measure how much moisture is coming out of the air, the mass flow of the air, inlet temperature, and outlet temperature. Since you have only measured one of those four parameters you can't really reach any conclusions.

  9. #8
    Join Date
    Aug 2012
    Posts
    3,849
    Post Likes
    maybe you should have bought a 60000 btu window shaker.