Results 1 to 2 of 2
  1. #1
    Join Date
    Nov 2007
    Posts
    11
    Post Likes

    Energy saving for resetting the AHU setpoint

    Energy saving for resetting the AHU setpoint

    I would like to seek someone help to solve the below problem.

    If the return air temperature setpoint of AHU re-adjust from 22oC to 24oC, how to calculate the energy saving of chiller
    ~ One Chiller cooling capacity & power input: 562 KW & 194.7KW
    ~ One AHU cooling capacity: 132KW
    ~ Return air temperature setpoint of AHU: 22oC

  2. #2
    Join Date
    Aug 2003
    Location
    Fort Worth, TX
    Posts
    11,794
    Post Likes
    Return air enthalpy, supply air enthalpy, and volume of air moving through air handler can help you on this problem. Since I'm an IP guy, the calculation would be 4.5 * CFM * enthalpy difference between return and supply. Run the numbers with your two different sets of return air set points to see what capacity difference is apparent. From there the difference would show up at the chiller.
    Building Physics Rule #1: Hot flows to cold.


    Building Physics Rule #2:
    Higher air pressure moves toward lower air pressure


    Building Physics Rule #3:
    Higher moisture concentration moves toward lower moisture concentration.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.