    Hello, I'm a fire marshal and fire investigator and I recently attended a fire involving what was called a peckerhead valve on a large rooftop unit. The peckerhead valve housing was apparently the source of the fire / explosion as the housing was obviously distended from the inside. Stupid question, what does the peckerhead do under normal conditions and how do they typically fail, especially in ways that can cause a fire?
    Also, in a separate and maybe related question, is it wise from a fire prevention point of view to retrofit R-600 refrigerant into old / existing equipment?
    Thank you!
    Mar 2013
    Billington Heights, NY
    a peckerhead is the common slang term for where compressor terminals originate. the wires connect here. loose connections and high amp draws can cause the connections to melt, opening a hole in the housing. in some instances, the ceramic holding the terminals can breach causing a conflagration of modern proportions when the compressor oil, refrigerant, and electrical sparks interact.
    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"
    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."
  3. Likes FM Mike liked this post
  4. #3
    Jul 2017
    Thank you HVAC_Marc. Very helpful!
  5. Likes HVAC_Marc liked this post
  6. #4
    Mar 2013
    Mike, here's an example of what can happen:
    http://hvac-talk.com/vbb/showthread....-largo-Florida
  7. #5
    Jul 2000
    Guayaquil EC
    Quote Originally Posted by FM Mike View Post
    ...Also, in a separate and maybe related question, is it wise from a fire prevention point of view to retrofit R-600 refrigerant into old / existing equipment?
    R600 (Isobutane) and R290 (Propane) should never be charged into any existing equipment which was not originally designed for those refrigerants.
    Check out Icemeister's Back Room
    Read My Latest Rambling:
    What Is Mechanical Subcooling?
    ...and a new calculator:
    Nitrogen Pressure Calculator
  8. Likes Ga-HVAC-tech liked this post
  9. #6
    Fort Worth, TX
    Large rooftop unit charged with R600? For real?? How badly was the building damaged by the ensuing fire?
    Also, fuel grade propane is inappropriate for ANY refrigeration system, even the small ones allowed to run refrigeration grade propane.
    Building Physics Rule #2:
    Building Physics Rule #3:
  10. #7
    Southeastern Pa
    Just to be clear...the Peckerhead is a connector for the compressor electrical supply.
    It is not a "valve."