Results 1 to 11 of 11
    Jul 2009
    Florida
    Amanaca AC + Honeywell thrmostat = no demudification
    I got a brand new 2 stage Amana AC witn a Honeywell VisionPro 8000 thermostat
    amana ASZC160481A 2 stage heat punp
    amana AVPTC61D14 air handler
    honeywell TH8321WF1001 thermostat
    The dehumdifier doesn't seem to be working at all
    I set the thermostat at 45% humidity but the AC only comes on when the temp goes over its 72 degree setting
    The humidity is always around 60+%.
    dehumidifier status on the display = wait
    I toggled the U1 setting in the thermostat between open/closed it says dehumidifying for a few minutes, then goes back to wait on either setting
    AC people are the best in town - or so I thought
    Is the thermostat compatible with this AC?
    Houston,Tx.
    Dehumidifier? You mean dehumidifier setting, or did you have an existing dehumidifier?
    X2
    How is this wired?
    Did they know to set it up to dehumidify?
    A quick internet search reveals that airhandler has a dehumidification feature. Sounds to me like something is not configured/installed correctly.
    Jul 2009
    Florida
    no external dehumidifier
    dehumidifier equipment setting on the thermostat = ac with low fan
    other choices are ac w/hi fan, dehumidifier, none
    next page on the thermostat option menu is humidifier wiring with one choice = tstat terminal u1.
    Next page gives u1 option = normally open or normally closed
    I tried them both and didn't mess with any other setting
    Houston,Tx.
    Quote Originally Posted by stevenestrada View Post
    None of these setting will work, these are for an external dehumidifier.
    Jul 2009
    Florida
    is the honeywell TH8321WF1001 thermostat compatible with the ac?
    amana ASZC160481A 2 stage heat pump
    yes?
    is ac w/low fan the right setting for dehumidify if no external dehumidifier?
    Houston,Tx.
    yes?
    Can't answer the first question, but your installer should know, or anyone that sells this equipment.
    Yes! is the answer to your second question...
    Do you understand those install diagrams?
    Additional work is needed to make ANY of those operate when stat is in dehum mode!!
    Jul 2009
    Florida
    Honeywell says the thermostat is compatible
    I got humidity set at 45,
    AC is running nonstop
    It hits the temp setting, stage 2 shuts down, stage 1 over cools three degrees, then kicks in to dehumdify mode - and sits there - running with nothing changing until stage 2 kicks in when the sun is over the roof
    Still humidity = 60
    The fan sounds like it slowing down in dehumidify mode
    Dealer came set the blower from A to B making it faster.
    If anything that should make the humidity worse
    Is there is some other setting we're missing
    Is there some hidden setting holding it at 60?
    Southold, NY
    Still humidity = 60
    Duct leakage
    house leakage
    Sensor(s) out of calibration
    oversized
    overcharged
    undercharged
    wrong fan speed(s)
    theres a lot of things. The installing contractor must find the reason.
    Jul 2009
    Florida
    Thanks for the the reply
    Leak test and ducts were cleared before installing the new ac and I blasted on the old on high the day before - humidity was 39
    There's a humidity sensor in the air handler?