    I have the exact same furnace at a home in Ontario.. That baby is upside down,,,,,,

  2. #15
    Join Date
    Oct 2003
    Location
    Edmonton
    Posts
    7
    Post Likes

    Hmm Upside Down

    Further to my last,,, It is a Keeprite 80BTU,, Horizontal (left or right only). Multi position furnaces were not tearing up the market at that time. The Induced Draft Fan must be mounted above burner, This one is not. Also notice the flue vent,,, attached in such as way at to vent upwards, but in no way anywhere close to manufacturers instruction,,, this installation was done by a couple of guys in a volkswagen showing up with all their tools still in the packaging,, and not having a clue,, but probably got the cheque off the customer. Why was it never inspected?,, Because the inspector for the utility is not about to go up into a crawl space or attic when his waist measurements exceed the size of the hatch.
    Regards

  3. #16
    Join Date
    Nov 2003
    Posts
    10
    Post Likes
    No really that is a retrofit I have done before, It is correct if the instructions are followed properly!!!

  4. #17
    Join Date
    Feb 2004
    Location
    atlanta,ga
    Posts
    24
    Post Likes
    Beleive it or not ducane says it can be installed like this go figure