    JCI Labeling Question on Controller Points List "CO OUT 1"

    They list UI IN-X, BI IN-X, AO OUT-X, BO OUT-X and CO-OUT-X. The others make sense, but I haven't seen CO OUT listed before. Am I correct thinking these would be part of the BACnet interface points and would stand for Communications Output, as opposed to a physical output?
    Thanks for any insights!

  2. #2
    Join Date
    Jun 2009
    Location
    StL, MO
    Posts
    691
    Post Likes
    Configurable Output (0-10Vdc or triac) hardware point.
    UA LU 562

  3. Likes bacnet>CCN liked this post
  4. #3
    Join Date
    Apr 2014
    Location
    MN
    Posts
    400
    Post Likes
    Thread Starter
    Excellent! Thanks much!