Results 1 to 10 of 10
  1. #1
    Join Date
    Sep 2016
    Location
    Saint Johnsville NY
    Posts
    23
    Post Likes

    Indigo Manitowoc

    Have a ID right as it goes in harvest I hear the hot gas open but the cond fan does not shut off. Now I ran manual a couple of time back and forth only 1 time did the fan cycle off. Also as it goes into harvest the txv flooding alarm show.
    It's makes ice beautiful when it get to harvest also so charge is not a worry I think.
    I am thinking the controller failed. I thought I heard the main controller relay chatter also.

    It just seems that when it call for harvest the hot gas and fan do not cycle correctly leading to a moan controller fault

  2. #2
    Join Date
    Mar 2007
    Location
    In the Conservatory with a Lead Pipe
    Posts
    14,645
    Post Likes
    Could be just a dirty condenser

  3. Likes DavidDeBord liked this post
  4. #3
    Join Date
    Sep 2016
    Location
    Saint Johnsville NY
    Posts
    23
    Post Likes
    Thread Starter
    Will that prevent unit for going into harvest? And I do have it scheduled to Clean in the morning when the place is not busy

  5. #4
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,457
    Post Likes
    If cleaning does not help, I would give Manitowoc tech support a call on Thursday.

    They may have a better way to determine if the controller is actually on its last legs.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  6. Likes DavidDeBord liked this post
  7. #5
    Join Date
    Mar 2007
    Location
    In the Conservatory with a Lead Pipe
    Posts
    14,645
    Post Likes
    If the compressor is energized the fan has the ability to run even in harvest. Dirty condenser or faulty fan cycling switch are very common.

  8. Likes DavidDeBord liked this post
  9. #6
    Join Date
    Sep 2016
    Location
    Saint Johnsville NY
    Posts
    23
    Post Likes
    Thread Starter
    Thanks. Used to the prodigy controller on Scots where it shuts the fan down.been to the Manitowoc class 3 years ago and dont remember much lol

  10. #7
    Join Date
    Mar 2007
    Location
    In the Conservatory with a Lead Pipe
    Posts
    14,645
    Post Likes
    Yeah Scotsman shut down a little before harvest or at least they used to. Not many Scotsman buy me unless it's a little Ice o matic

  11. Likes DavidDeBord liked this post
  12. #8
    Join Date
    Sep 2016
    Location
    Saint Johnsville NY
    Posts
    23
    Post Likes
    Thread Starter
    Just update looks to be having a hot gas valve sticking damn thing

  13. #9
    Join Date
    Sep 2016
    Location
    Saint Johnsville NY
    Posts
    23
    Post Likes
    Thread Starter
    Damn intermittent failures put a new hot gas valve in and working like a champ again

  14. #10
    Join Date
    Mar 2007
    Location
    In the Conservatory with a Lead Pipe
    Posts
    14,645
    Post Likes
    Be happy...
    you didn't put a new board in