    Quote Originally Posted by rundawg View Post
    You are too bore sighted on the start capacitor, and neglecting the most important part of the start kit - the potential relay.

    Most start capacitor failures are due to the potential relay not opening once the compressor comes up to speed.

    Trane has very specific pick up, drop out, and continuous voltages for their potential relays, and the reason OEM parts are recommended for their units.

    While either of those 5-2-1's will probably work, you should install only OEM parts if you are concerned about potential failures during triple digit temps.
    Ah thank you! This was a very helpful reply! Ok so makes sense that I should keep the potential relay the same, I didn't realize they could vary that much. Thank you!

  2. #15
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    9,189
    Post Likes
    Quote Originally Posted by breakc0de View Post
    Ah thank you! This was a very helpful reply! Ok so makes sense that I should keep the potential relay the same, I didn't realize they could vary that much. Thank you!
    Instead of learning the tricks of the trade, learn the trade.

  3. #16
    Join Date
    Jan 2004
    Location
    PA
    Posts
    74,863
    Post Likes
    This is not a DIY site.

    Thread closed.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.