Results 1 to 7 of 7
    Jun 2018
    Vulcan range with excessive carbon
    Hey there.
    Ive had two calls on two of the same ranges in two different locations the past week and the problem is confusing the crap out of me.
    Alright so the issue im having is in the burner of the range section of the oven. When I got to both units the burner is so full of carbon that the flame catches at the air shutter and the entire inside of the oven is caked. I cleaned it up to the best of my ability and got it working again no problem, however, a week later i get a call back with the same issue.
    - one unit is at 10.5” wc and the other at 11” wc. I tap into the top burner section but as i adjust the regulator on the back of the appliance the gas pressure doesnt change. The manufacturer spec calls for 10” wc, but i cannot adjust it.
    - a work associate thought there was inadequate make up air and to check by letting all burners go on full heat for 15 minutes and to see if hot air is blowing out the bottom, I did this and it did not come out.
    Im not the most familliar with Vulcan and the tech support suggested a new thermostat, this is very costly and it doesnt make sense that itd help anything.
    The model on the unit is 36S-6BP. It uses propane as a fuel.
    Mar 2013
    Billington Heights, NY
    long high yellow flames often indicate a lack of combustion air.
    This forum requires that you wait 20 seconds between posts. Please try again in 50 seconds.
    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"
    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."
    Jun 2018
    Quote Originally Posted by HVAC_Marc View Post
    Air shutter is fully open. I talked to someone today that said that the burner may be “blown”, some holes are larger than others over time and can cause uneven flame height which would in term cause my issue.
    Mar 2013
    I was thinking something similar after I posted it. Cracked burners sometimes exhibit the same problem.
    Oct 2008
    Have you checked the orifice hole size? You can easily gauge the orifice size with an orifice bit set. Maybe someone mistakenly drilled the orifice for natural gas instead of propane. I suggest checking that.
    "You never know what others don't know." -
    If I can't laugh at myself...then I'll laugh at YOU! -
  6. Likes HVAC_Marc liked this post
  7. #6
    Mar 2013
    maybe it was never converted properly.
  8. #7
    Jan 2016
    The triangle in the Keystone
    Pull the orifice and check it. I don’t know your model number but I’d expect to see a number 53 orifice in a range top.
    When you cleaned the soot did you pull the burners? I’ve found if you don’t get it all in the first cleaning it can come back to haunt you.
    Make sure your gas pressure is 10” dynamic. I know your pretty close right now and it might seem insignificant but even a .5” off for some LP commercial kitchen equipment can be problematic.