    Split condenser header

    A picture would say it all, but I can't post those yet. A particular customer's rack has two condensers, each split into four sections. Each section has ball valves. They manually valve off some condensers over the winter. One of the valved-off ones blew a nice-sized hole in the liquid header. Both headers have bulged spots. Apparently refrigerant migrated past the ball valves and the condenser got chock full of liquid, which doesn't compress very well when it gets warmer outside. So, condenser quoting time.

    Kind of gives a new meaning to the phrase split condenser.

  2. #2
    Join Date
    May 2017
    Posts
    5
    Post Likes
    Thread Starter
    I should add that we didn't set it up, and they do most of their own work. Not sure why they don't have a split condenser valve.

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,437
    Post Likes
    Sent the Pics to my email (In my Profile) I have to see this.

  4. Likes HVAC_Marc liked this post
  5. #4
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    17,941
    Post Likes
    post em up!
    This forum requires that you wait 20 seconds between posts. Please try again in 50 seconds.

    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"

    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."

  6. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,437
    Post Likes
    Quote Originally Posted by HVAC_Marc View Post
    post em up!
    Id love to but I dont have them!

















    In the mean time does this work?
    Attached Images Attached Images  

  7. #6
    Join Date
    Mar 2013
    Location
    Billington Heights, NY
    Posts
    17,941
    Post Likes
    This forum requires that you wait 20 seconds between posts. Please try again in 50 seconds.

    Experience - knowing when to get the hell out of the way and plug your ears. "Don't be a sissy. Turn it on!"

    Poodle Head Mikey - "the world is well populated with the unknowing and the uncaring and the stupid."

  8. Likes pecmsg liked this post
  9. #7
    Join Date
    May 2017
    Posts
    5
    Post Likes
    Thread Starter
    pecmsg has pics.

  10. #8
    Join Date
    Sep 2002
    Posts
    21,876
    Post Likes
    There is a code I believe which makes this illegal. Anything which can contain hydraulic pressure and be valved off must have a relief valve fitted to the can-be-isolated section.

    PHM
    ------



    Quote Originally Posted by disciple View Post
    A picture would say it all, but I can't post those yet. A particular customer's rack has two condensers, each split into four sections. Each section has ball valves. They manually valve off some condensers over the winter. One of the valved-off ones blew a nice-sized hole in the liquid header. Both headers have bulged spots. Apparently refrigerant migrated past the ball valves and the condenser got chock full of liquid, which doesn't compress very well when it gets warmer outside. So, condenser quoting time.

    Kind of gives a new meaning to the phrase split condenser.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  11. #9
    Join Date
    Oct 2014
    Location
    Columbus, Ohio
    Posts
    1,096
    Post Likes
    I've heard of this being a way to control condenser size in cold weather, but I always assumed that the solenoids or ball valves would only be on the condenser inlet, and the outlet would remain open and connected to the system to prevent this sort of failure. Why would they close off both ends of the condenser sections that they wanted to disable?

  12. #10
    Join Date
    Mar 2008
    Location
    kansas
    Posts
    408
    Post Likes
    We had one that didn’t have a spit condesor valve manual valves on both the discharge and liquid but had a pump out line to the suction header that was left open. This was old school rack held like 2500# of 502
    Honeywell you can buy better but you cant pay more

    I told my wife when i die to sell my fishing stuff for what its worth not what i told her i paid for it

  13. Likes rjk_cmh liked this post
  14. #11
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,155
    Post Likes
    The whole point of splitting the condenser is to minimize the condenser flooding charge requirement and only experience will teach you that ball valves aren't guaranteed for 100% positive shutoff.

    Here's the proper way to pipe the condenser using a 3-way heat reclaim type solenoid valve, check valves and a condenser pumpout bleed line with a capillary tube to regulate liquid flow into the suction header.

    Name:  Split-Condenser-Piping-Hussmann-2013.png