Quote Originally Posted by Benji85 View Post
Hello,
I cant tell if that was sarcasm or a serious question so in the spirit of light heartedness I will respond with this:

testing from all three legs comes back with 207.9v between legs 1 & 2, 208.1 between 1&3 and 207.9 between 2 & 3. using the reset rocker sends it through the reset but comes right back to external stop/ sol ckt 1 / flow interlock. all of which trane came and verified were not the actual issue and could not figure out what was causing it to not engage.
It was kind of a "haha". It's always the first thing tech support says.

Good to know that the power is good and that a power/phase monitor isnt tripping it.