    Superheat question

    I’m having a brain fart right now.

    R-448a WIF
    Suction temp at evap 7deg
    Suction pressure at evap 11 psi = -18 deg dew
    7 minus -18 = 25. I have 25 deg SH at my evap. Does that sound right?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    13,895
    Post Likes
    With 404 I come up with 34*f

  3. #3
    Join Date
    Sep 2013
    Location
    Atlanta, GA
    Posts
    1,281
    Post Likes
    Quote Originally Posted by VanMan812 View Post
    I’m having a brain fart right now.

    R-448a WIF
    Suction temp at evap 7deg
    Suction pressure at evap 11 psi = -18 deg dew
    7 minus -18 = 25. I have 25 deg SH at my evap. Does that sound right?
    Your math is correct (I didn't get my PT chart out to verify that part).

  4. #4
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,049
    Post Likes
    I try to imagine a number line when dealing with subtracting a negative number. Start at -18 and couynt how many numers there are to get to +7...ie, 25

    -18 -17 -16 -15 -14 -13 -12 -11 -10 -9 -8 -7 -6 -5 - 4 -3 -2 -1 0 +1 +2 +3 +4 +5 +6 +7

  5. Likes DavidDeBord liked this post
  6. #5
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    775
    Post Likes
    Thread Starter
    I was thinking I need to compensate for the glide. Yes?


    Sent from my iPhone using Tapatalk

  7. #6
    Join Date
    May 2015
    Location
    CT
    Posts
    3
    Post Likes
    25degree superheat is way too much on freezer. Is it new install?

  8. #7
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,049
    Post Likes
    Quote Originally Posted by VanMan812 View Post
    I was thinking I need to compensate for the glide. Yes?


    Sent from my iPhone using Tapatalk
    No, the dewpoint is the saturation temperature of the refrigerant gas leaving the evaporator, so by definition, the superheat is the measured temperature minus the dewpoint temperature.

    Some guys have been using the midpoint or average evap temperature to determine superheat, but that isn't the way to do it properly.

  9. Likes DavidDeBord liked this post
  10. #8
    Join Date
    Jan 2016
    Location
    The triangle in the Keystone
    Posts
    775
    Post Likes
    Thread Starter
    Quote Originally Posted by icemeister View Post
    No, the dewpoint is the saturation temperature of the refrigerant gas leaving the evaporator, so by definition, the superheat is the measured temperature minus the dewpoint temperature.

    Some guys have been using the midpoint or average evap temperature to determine superheat, but that isn't the way to do it properly.
    That makes sense and that’s what I usually do. The p/t chart I was using gave the average temp (bubble and dew) and it made me think for a minute that I should be using that instead of the dew.

    Why are some guys using the midpoint? Wouldn’t that give a false SH that’s higher than it actually is? That’s a slippery slope.


    Sent from my iPhone using Tapatalk

  11. Likes DavidDeBord liked this post
  12. #9
    Join Date
    Jun 2011
    Location
    NE Ohio
    Posts
    98
    Post Likes
    Quote Originally Posted by VanMan812 View Post
    I was thinking I need to compensate for the glide. Yes?


    Sent from my iPhone using Tapatalk
    https://www.honeywell-refrigerants.c...012&download=1

  13. #10
    Join Date
    Jul 2000
    Location
    Guayaquil, EC
    Posts
    13,049
    Post Likes
    Quote Originally Posted by VanMan812 View Post
    That makes sense and that’s what I usually do. The p/t chart I was using gave the average temp (bubble and dew) and it made me think for a minute that I should be using that instead of the dew.

    Why are some guys using the midpoint? Wouldn’t that give a false SH that’s higher than it actually is? That’s a slippery slope.


    Sent from my iPhone using Tapatalk
    It's been mentioned a couple of times in recent threads by some market techs that the chain they do work for requires they use the midpoint for superheats with blends because the cases run better and are more able to meet the design temps. I don't agree with that method as it's not technically correct. It may work for them but not for the reason they think. The techs say they're just doing as they're told...and you can't knock that too much.

  14. Likes DavidDeBord liked this post