    YORK AIR SCREW CHILLER...ALL COMPRESSORS OUT ON LOW SUCTION

    Hey All,

    Need quick info. York Air-Cooled Screw Latitude 500ton Chiller

    I've never actually worked on a York Lat before so I'm looking for someone who's had to deal with these. Back story, These units sat crated for year+ due to construction delays and then sat additional year+ after installation prior to commissioning because of more delays. A chiller ran for 3 days before all four compressors failed on Low Suction. We test ran it again until compressors alarmed out on Low Suction to see if we good determine anything. I either have a leak (all four) or a blockage (on all four). I do not have the equipment on hand to deal with 400 lbs of R134 so I will check anything before tearing into the evap.

    Anyways, before I tell them how F'd they are on a brand new (5 year old) chiller. I want to make sure I'm not missing something that ISN'T in the troubleshooting procedures. My recommendation was to bring in a York guy to re-commission these units so they have documentation for the inevitable lawsuits.

    FYI_NO OIL SIGNS.

    Suggestions?

  2. #2
    Join Date
    Sep 2002
    Posts
    22,054
    Post Likes
    What is the flow rate through the chiller?

    PHM
    ------


    Quote Originally Posted by HDog View Post
    Hey All,

    Need quick info. York Air-Cooled Screw Latitude 500ton Chiller

    I've never actually worked on a York Lat before so I'm looking for someone who's had to deal with these. Back story, These units sat crated for year+ due to construction delays and then sat additional year+ after installation prior to commissioning because of more delays. A chiller ran for 3 days before all four compressors failed on Low Suction. We test ran it again until compressors alarmed out on Low Suction to see if we good determine anything. I either have a leak (all four) or a blockage (on all four). I do not have the equipment on hand to deal with 400 lbs of R134 so I will check anything before tearing into the evap.

    Anyways, before I tell them how F'd they are on a brand new (5 year old) chiller. I want to make sure I'm not missing something that ISN'T in the troubleshooting procedures. My recommendation was to bring in a York guy to re-commission these units so they have documentation for the inevitable lawsuits.

    FYI_NO OIL SIGNS.

    Suggestions?
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  3. #3
    Join Date
    May 2018
    Location
    OCONUS
    Posts
    10
    Post Likes
    Thread Starter
    Pump under VFD but never deviates from 30% so it appears that the VFD is locked at 30%.

  4. #4
    Join Date
    May 2018
    Location
    OCONUS
    Posts
    10
    Post Likes
    Thread Starter
    300GPM per pump

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,960
    Post Likes
    Are you a Tech or Maintenance Man on Site?

    You need 1500 GPM

  6. #6
    Join Date
    May 2018
    Location
    OCONUS
    Posts
    10
    Post Likes
    Thread Starter
    Where did you come up with 1500 GPM? Do you have a link to the table that states the values? The manual I have merely states cooler GPM is MIN-400 GPM and MAX-1400 GPM.

  7. #7
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,960
    Post Likes
    3GPM per Ton on average.

    Your manual stated 1400. I'd say i was close

  8. #8
    Join Date
    Sep 2002
    Posts
    22,054
    Post Likes
    I would unlock the VFD.

    "locked at 30%" being correct for the chillers would mean that the pumps are 300% larger than they have to be - which seems very unlikely to have been specified.

    PHM
    -------


    Quote Originally Posted by HDog View Post
    Pump under VFD but never deviates from 30% so it appears that the VFD is locked at 30%.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  9. #9
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,430
    Post Likes
    I want to re-ask that one germaine question.... are you an HVAC technician, or are you an on-site maintenance man?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  10. #10
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,960
    Post Likes
    Quote Originally Posted by timebuilder View Post
    I want to re-ask that one germaine question.... are you an HVAC technician, or are you an on-site maintenance man?
    Now that’s a tough one to answer.

  11. #11
    Join Date
    May 2018
    Location
    OCONUS
    Posts
    10
    Post Likes
    Thread Starter
    Rule of thumb. Doesn't work correctly with VSD compressors and pumps on VFD because demand and GPMs are supposed to fluctuate.

  12. #12
    Join Date
    May 2018
    Location
    OCONUS
    Posts
    10
    Post Likes
    Thread Starter
    I agree with the assumption. After I brought up the concern regarding pumps "seem to be locked at 30%" amazingly they are now fluctuating. Yes, others have access to DDC. I'm caught in the middle of a bunch of egos and insecurities.

  13. #13
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,942
    Post Likes
    Quote Originally Posted by pecmsg View Post
    3GPM per Ton on average.

    Your manual stated 1400. I'd say i was close
    3 GPM per ton is average for water cooled condenser. 2.4 GPM per ton is nominal for chilled water which will give you a 10 delta T At full load. Many new sites have lower flow rates and higher delta T but I agree 30% on VFD is way too low.

    Quote Originally Posted by Poodle Head Mikey View Post
    I would unlock the VFD.

    "locked at 30%" being correct for the chillers would mean that the pumps are 300% larger than they have to be - which seems very unlikely to have been specified.

    PHM
    -------
    The flow rate is not linier to speed, it’s squared so 30% = 18 HZ which means there is about 5% flow going through the chiller if the pump was sized correctly.

    Quote Originally Posted by timebuilder View Post
    I want to re-ask that one germaine question.... are you an HVAC technician, or are you an on-site maintenance man?
    You’ve been asked this question twice and seem to be dodging it. Are you a chiller tech or maintenance?
    The 2nd most important amendment is to protect the 1st...