    Trans voyageR RTHM BOARD LOCKOUT

    We have a 1 year old trane voyagerwith RTHM BOARD. The unit is locking out with cool fail. We checked pressures temps. All looks good when its running. We were having issue with it blowing condensor fan fuses. We replaced fan motor. It looks like it just has high prrssure,low pressure,discharge line temp. The unit is on a bas. It just has normal y1,y2 etc. I had 2 flashes on led 2 today. I reset it runs fine. Does unit go in LOCKOUT on first pressure switch trip. Does it LOCKOUT both stages if it sees high pressure on just first stage. The unit model is a ysd300g. I though about putting tattletales on. Any suggestions??

  2. #2
    Join Date
    Apr 2018
    Posts
    23
    Post Likes
    You can check the low voltage circuit at the J1 plug on the RTRM module for devices on each circuit. Check continuity through the entire circuit to see that all devices are closed. If one circuit trips the other will still run. Check the ESTOP and compressor disable on LTB. If something is opening on ESTOP then yes the entire unit will shutdown. Good luck

  3. #3
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,239
    Post Likes
    What are your typical outdoor ambient temps, and what is your condenser delta T?
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  4. #4
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    16,715
    Post Likes
    Trane's typical lock out procedure goes like this:

    It takes three trips of the safety in any one hour rolling period.
    If you were a real tech, you'd solder a relay on that board and call it good to go.

  5. #5
    Join Date
    Jan 2001
    Posts
    840
    Post Likes
    Thread Starter
    To be honest today was first time I was there. I was on another call close and went to lend a hand as this has been an ongoing issue. Both stages were off reset unit and both came on. The low voltage part of PHASE monitor is on estop. I guess my thoughts are either something funky with condensor fans where it knocks both circuits off or PHASE monitor. Another tech checked pressures and said they were ok.

  6. #6
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    16,715
    Post Likes
    With the circuit boards they use nowadays, it is very likely the tattle tales won't trip, not enough current is flowing.

    So, instead, you use 1/100 amp fuses. Get them online, then buy the fuse holders at your local auto store. A few months back I put them on a unit with intermittent problems and proved it was the high pressure tripping that circuit off line.


    Quote Originally Posted by hvac17011 View Post
    We have a 1 year old trane voyagerwith RTHM BOARD. The unit is locking out with cool fail. We checked pressures temps. All looks good when its running. We were having issue with it blowing condensor fan fuses. We replaced fan motor. It looks like it just has high prrssure,low pressure,discharge line temp. The unit is on a bas. It just has normal y1,y2 etc. I had 2 flashes on led 2 today. I reset it runs fine. Does unit go in LOCKOUT on first pressure switch trip. Does it LOCKOUT both stages if it sees high pressure on just first stage. The unit model is a ysd300g. I though about putting tattletales on. Any suggestions??
    If you were a real tech, you'd solder a relay on that board and call it good to go.

  7. #7
    Join Date
    Apr 2018
    Posts
    23
    Post Likes
    Gonna have to troubleshoot further, need more information to help. The phase monitor interrupts 24VAC to entire unit. Maybe something with the phase monitor? Don't know, need to dig a little deeper. Your issue doesn't sound like anything with condenser fans.

  8. #8
    Join Date
    Jan 2001
    Posts
    840
    Post Likes
    Thread Starter
    I went onsite again today unit running. The old unit or the other units do not have the icm power monitor control on it. This entire street has history of voltage fluctuations. I reset a wshp on a under/over voltage code at another building yesterday Input voltage was fine. I looked at info on line. It appears as the icm control will autoreset but it locks trane board out. I decided to bypass it for now. We are going to put a recorder on incoming power. We may wire it in different other than on emergency off contact. Did i do correct thing maybe maybe not. Everyone else just resets it. Time will tell.