    Hi. Can I swap 12uF and 12.5uF for a blower? Will doing so cause any issue?

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    14,463
    Post Likes
    Read:
    Attached Images Attached Images

  3. Likes HVAC/R 19 liked this post
  4. #3
    Join Date
    Nov 2006
    Location
    Southeastern Pa
    Posts
    28,239
    Post Likes
    Changing a capacitor from the value determined by the motor manufacturer usually raises the current drawn by the motor, and because of that, increases the heat the motor creates, which can shorten motor life.


    You can use a different value temporarily, until you reach starbase for a new cap, since they can't be replicated.
    Last edited by timebuilder; 05-14-2018 at 08:30 AM.
    [Avatar photo from a Florida training accident. Everyone walked away.]
    2 Tim 3:16-17

    RSES CMS, HVAC Electrical Specialist
    Member, IAEI

    AOP Forum Rules:







  5. Likes HVAC/R 19 liked this post
  6. #4
    Join Date
    Nov 2016
    Posts
    36
    Post Likes
    Thread Starter
    So, .5 will make a difference?

  7. #5
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    5,050
    Post Likes
    Quote Originally Posted by hvactrekkie View Post
    So, .5 will make a difference?
    Yes.


    Sent from my iPhone using Tapatalk

  8. #6
    Join Date
    Apr 2018
    Location
    Rhode Island
    Posts
    80
    Post Likes
    Not if you use the + or - 5% rule. I've seen 6% and 10% used also.When in doubt,get the exact replacement!

  9. #7
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    3,412
    Post Likes
    I doubt his 12.5 is even 12.5 to begin with. More like 12.3 out of the box. And if it is exactly 12.5. It won't be for long. That's why the cap manufacturer puts the +or- on the box because they can't guarantee it to be on the money. The rule for replacement is + or minus 10%. I think you'll be OK.

  10. Likes ChuckDe liked this post
  11. #8
    Join Date
    May 2018
    Location
    San Fernando Valley, CA
    Posts
    70
    Post Likes
    What about sizing up a compressor capacitor. Let’s say 5-10 mfds. Increases heat as well?

  12. #9
    Join Date
    Feb 2006
    Location
    Phoenix,AZ
    Posts
    3,412
    Post Likes
    Quote Originally Posted by OGlad View Post
    What about sizing up a compressor capacitor. Let’s say 5-10 mfds. Increases heat as well?
    You can't go 10 mfd. It defies the rule. As 10% of a 80 mfd is 88 not 90.

  13. #10
    Join Date
    Sep 2016
    Posts
    37
    Post Likes
    99,9 % sure, you can swap them, no problem.

  14. #11
    Join Date
    Sep 2016
    Posts
    37
    Post Likes
    Sorry I forgot, may be you know, The isolation voltage must be equal or bigger in the new cap.

  15. #12
    Join Date
    Jul 2010
    Location
    Andalucia
    Posts
    4,379
    Post Likes
    If a 12uf capacitor isn't ok to swap for a 12.5 is a 12.5 rated cap reading 12 ok? I agree that you should always use the proper cap and if you do swap a 12 for a 12.5 you should note it for future reference. It is also always a good idea to take a reading of the new cap
    Benghazi was a 4 year investigation, there were zero indictments. The Clinton emails was a 2 year investigation, there were zero indictments. The Mueller investigation has been 12 months, there have been 23 indictments.

    When 11 American prisoners in North Korea were released during the Obama administration, the President didn’t make it into a spectacle about himself.

    Trump was right Roseanne is about you.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  

Related Forums

Plumbing Talks | Contractor MagazineThe place where Electrical professionals meet.